Question: Gutter size question? I have three under ground existing 4" conduits and on the one line it request a gutter and then I can come out of the top of the gutter with two 4'' pips to feed the new panel.314.28 its says for a strait pull 8x the largest pip size so 8 x 4'' =32 and for my cross section 6x so 6 x 4'' =24 + 4'' +4'' = 32So I need a 32x32 gutter?pretty big for just a strait pull please tell me I am wrong!
The cross sectional area for the gutter should be 32 square inches. The gutter size would be 8"x4" or 6"x5.33". Flag for review