Question: Hello,I am considering moving my laundry from the basement to the living level. (Gotta keep the wife happy).I have two questions1) How far is too far to run 10/3 cable? It looks like I will need about 70' to get from the box to the new dryer point.2) If the distance is not too far, do I have to drill every floor joist or can I nail up so 1x4 and surface mount the cable?
1) Distance for 10/3 Cable
For 10/3 cable, the maximum allowable distance for a 240-volt dryer connection is 100 feet. However, it's recommended to keep the distance as short as possible to minimize voltage drop. In your case, 70 feet is well within the acceptable range.
2) Cable Routing
You can surface mount the cable on a 1x4 if it is properly secured and protected. However, you must still drill through the floor joists at regular intervals for support and to prevent the cable from sagging. The National Electrical Code (NEC) requires that cables be supported every 4.5 feet for vertical runs and every 12 feet for horizontal runs.
Recommended Approach
1.
Verify Wire Size
Ensure that you are using 10/3 cable rated for at least 30 amps.2.
Plan the Route
Choose the shortest and most direct path from the electrical box to the dryer point.3.
Drill Pilot Holes
Mark the locations of the floor joists and drill pilot holes every 4.5 feet.
4.
Secure the Cable
Run the cable through the pilot holes and secure it to the floor joists using NM staples or cable clamps.5.
Mount the 1x4
Attach the 1x4 to the floor joists and surface mount the cable on top.6.
Cover the Cable: Install a cable cover or raceway to protect the cable and provide a neat appearance. Flag for review