Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Residential circuit - UF in EMT

User: chrisrappl, Location: Raleigh

Asked on: Saturday, March 12, 2011 at 6:25 pm EST
Answered on: Tuesday, May 14, 2024 at 2:44 am EDT

Question: I have a residential job where the owner has asked me to run a 240v-20a circuit from the main panel to the 3rd floor for a PTAC unit. The panel is outside and he wants to run EMT on the exterior of the house up to the attic and then continue the cable, through the studs unspliced to the receptacle box.Can I run 12-2 UF in 1/2" EMT? I believe that 340.10 (3) allows me to, however I don't think that I can satisfy 340.24 (bending radius of 5X) if I use an LB to enter the building.I would use rain tight compression fittings, mineralacs to keep the conduit off of the wall and UF cable since the inside of the conduit is a damp location. The UF cable would continue unspliced through drilled studs to a NEMA 6-20R which would provide the disconnection means for the PTAC unit.

Yes, you can run 12-2 UF cable in 1/2" EMT.NEC Requirements



340.10(3)

UF cable is permitted to be installed in EMT if the EMT is threaded with a listed threadless rigid metal conduit fitting.


340.24(B)(1)(a)

The minimum bending radius for Type EMT is 5 times the trade size of the conduit. However, this requirement does not apply to elbows with radii of less than 5 times the conduit diameter (e.g., LBs).

LB Requirements

You can use an LB to enter the building, but it must be a

liquidtight LB
to prevent moisture from entering the conduit. You should seal the LB with a raintight sealant or putty to further enhance moisture protection.

Other Considerations



Mineralac spacers

Use mineralac spacers to keep the conduit at least 1/4" from the wall to prevent condensation buildup.


UF cable jacket

Ensure that the UF cable jacket is in good condition and free of any cuts or abrasions.*

Disconnection means

The NEMA 6-20R receptacle you mentioned serves as the required disconnection means for the PTAC unit.

Conclusion:


You can run 12-2 UF cable in 1/2" EMT for the exterior and interior portions of the circuit, even if you need to use an LB to enter the building. By using liquidtight fittings, raintight compression fittings, and mineralac spacers, you can ensure a safe and compliant installation. Flag for review

Previous Question Next Question