Topic: 200 panel with another 200 amp subpanel ?

User: Part-Time, Location: Houston, Texas

Asked on: Saturday, March 12, 2011 at 11:23 pm EST
Answered on: Tuesday, May 14, 2024 at 2:45 am EDT

Question: is it possible to run another 200 amp sub panel from the original 200 amp panelto power a storage building.

Yes, it is possible to run another 200-amp sub-panel from the original 200-amp panel to power a storage building. However, several factors need to be considered to ensure the safety and proper functioning of the electrical system.1. Electrical Load Calculation

Determine the total electrical load required for the storage building, including lighting, appliances, tools, and any other equipment. Ensure that the combined load does not exceed 200 amps.2.

Circuit Breaker Sizing

The sub-panel should have a main circuit breaker rated for 200 amps to match the rating of the original panel. Individual branch circuits within the sub-panel must be sized appropriately for the connected loads.3.

Wire Size and Type

Select appropriately sized wires based on the electrical load and distance to the storage building. Use copper or aluminum conductors rated for the amperage of the circuit. For example, 2/0 AWG (American Wire Gauge) copper wires are typically used for 200-amp circuits.4.

Conduit or Raceway

Protect the wires by installing them in a conduit or raceway. This provides mechanical protection and prevents damage or exposure to the environment.5.

Grounding and Bonding

Properly ground the sub-panel and all electrical equipment within the storage building to ensure safety and minimize the risk of electrical shocks.6.

Installation and Inspection

Hire a qualified electrician to install the sub-panel and wiring according to electrical codes and safety standards. Have the installation inspected to ensure compliance and safety.7.

Capacity of Original Panel

Verify that the original 200-amp panel has sufficient capacity to supply the additional 200 amps for the sub-panel. This includes considering the existing loads on the original panel and the potential for future expansion.8.

Distance and Voltage Drop:
The distance between the original panel and the storage building can affect the voltage drop in the wiring. Ensure that the voltage drop is within acceptable limits to prevent equipment malfunction or damage.By carefully considering these factors and following proper electrical practices, it is possible to run another 200-amp sub-panel from the original 200-amp panel to power a storage building safely and effectively. Flag for review