Question: Hey I recently purchased a home and took a look inside the breaker box...There is a #2 stranded copper that goes outside and is grounded to 2 Ground rods6 feet apart. This ground is not bonded to the neutral Then I took a look inside the Meter box/Disconnect and found another #2 copper bonded to the neutral, this ground goes inside to my Main Breaker panel an is bonded to the # 2 copper that goes outside to the 2 ground rods.Is this acceptable?
The grounding system you described is not acceptable according to the National Electrical Code (NEC) and may pose a safety hazard.
NEC Requirements
The neutral system must be bonded to the grounding electrode system at the service entrance. The grounding electrode system must consist of at least two grounding electrodes driven into the earth at least 6 feet apart. The grounding electrodes must be bonded together.
Your System
The neutral is not bonded to the grounding electrode system at the service entrance. The grounding electrode system consists of two grounding rods driven into the earth, but there is no bond between them.
Issues
Without a bond between the neutral and the grounding electrode system, fault currents can find an unintended path through your home, increasing the risk of electrical shock. The separate grounding rod at the breaker box is not properly bonded to the main grounding electrode system, which can create ground loops and interfere with proper grounding.
Corrective Actions
To bring your grounding system into compliance with the NEC, you need to: Bond the neutral to the grounding electrode system at the service entrance. Bond the two grounding rods together. Remove the separate grounding rod at the breaker box.
Recommendation:
It is highly recommended that you have a qualified electrician inspect your electrical system and make the necessary corrections to ensure the safety of your home. Flag for review