Topic: Motor on generator

User: john d, Location: Florida

Asked on: Thursday, March 17, 2011 at 9:08 am EDT
Answered on: Tuesday, May 14, 2024 at 2:55 am EDT

Question: How do i calculate the generator requirments for a motor. I have an existing building with a existing 150kw 188kva label rated 520amp generator. They have an existing fire pump 30hp, 3phase, code F, S.F. 1.15, 208v motor. They want to continue to add to the generator. Do i use 430.7 and use LRA. That would be 167.7 kva leaving 20kva for other loads?

To calculate the generator requirements for a motor, you can use the following steps:1. Determine the motor's load

This is the amount of power that the motor will draw from the generator. For a fire pump, you can use the following formula:

Load (kW) = Motor horsepower x Service factor
In this case, the motor horsepower is 30 and the service factor is 1.15, so the load is:
Load (kW) = 30 hp x 1.15 = 34.5 kW
2.


Convert the load to kVA

To do this, you will need to multiply the load in kW by the power factor of the motor. For a 3-phase motor, the power factor is typically 0.8.
Load (kVA) = Load (kW) / Power factor
In this case, the load is:
Load (kVA) = 34.5 kW / 0.8 = 43.1 kVA
3.


Add the locked rotor current (LRA) to the load

The LRA is the current that the motor will draw when it is first started. This current can be several times higher than the full-load current. For a 3-phase motor, the LRA is typically 6 times the full-load current.
LRA (amps) = Full-load current (amps) x 6
In this case, the full-load current is 520 amps, so the LRA is:
LRA (amps) = 520 amps x 6 = 3120 amps
4.


Convert the LRA to kVA

To do this, you will need to multiply the LRA by the line voltage. For a 208V motor, the line voltage is 208V.
LRA (kVA) = LRA (amps) x Line voltage (V) / 1000
In this case, the LRA is:
LRA (kVA) = 3120 amps x 208V / 1000 = 652.9 kVA
5.


Add the LRA to the load to get the total generator requirement:
Total generator requirement (kVA) = Load (kVA) + LRA (kVA)
In this case, the total generator requirement is:
Total generator requirement (kVA) = 43.1 kVA + 652.9 kVA = 696 kVA
Therefore, the existing 150kW 188kVA generator will not be sufficient to power the fire pump and any additional loads. You will need to upgrade to a larger generator. Flag for review