Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: bank calculation example in 2005 nec prep book

User: electricalperson, Location: massachusetts

Asked on: Thursday, March 17, 2011 at 1:37 pm EDT
Answered on: Tuesday, May 14, 2024 at 2:56 am EDT

Question: doing the bank service calculation in the book it shows the heat at 10kWdoing the AC/heat calculation, the ac is 10 hp at 230vthe ac is 230 x 50 = 11500va. i am going to use the 11500va ac load as the calculation since the heat wont be on at the same time.but in the book it shows the heat in the picture at 10kw but in the calculation it has the heat at 15kw.only thing i find in the code is branch circuit calculations for fixed electric space heating must be calculated at 125% because its a continuous load.i dont know where the 15kw came from do you think its an error in the book?

Yes, it is likely an error in the book. The code requires that branch circuit calculations for fixed electric space heating must be calculated at 125% because it is a continuous load. Therefore, the heat load should be 10 kW x 1.25 = 12.5 kW, not 15 kW. Flag for review

Previous Question Next Question