Question: I am a littlerconfused by code section 358. Can EMT ever be run in a slab/in a concrete deck or does it always have to RGS? Thanks.
EMT may be run in a slab/in a concrete deck, but it must be protected with a rigid metal conduit or intermediate metal conduit (IMC) for a distance of not less than 6 ft from the point where the EMT emerges from the slab/concrete deck. (358.10(A)(5)) Flag for review