Question: What is the correct way to size motor overloads for a motor that has no nameplate? I understand that overloads are to be sized by the motor nameplate FLA, but cannot find anything in code regarding if nameplate is missing. My assumption would be to use the NEC Table FLA value and multiply by 115%. Thoughts?
NEC Requirements
The National Electrical Code (NEC) requires motor overloads to be sized according to the motor's nameplate full-load amps (FLA). However, it does not explicitly address the case of a missing nameplate.
Industry Practice
In the absence of a nameplate, it is common industry practice to estimate the FLA using one of the following methods: Table FLA
Use the FLA value specified in NEC Table 430.247 for the motor's horsepower, voltage, and speed. Multiply the FLA by 1.15 to account for a 15% safety factor.
Measured Current
Use an ammeter to measure the current drawn by the motor at full load. This method is more accurate but requires special equipment and expertise.
Recommended Approach
It is advisable to consult with the motor manufacturer or a qualified electrician to determine the appropriate overload size. However, if this is not possible, the following approach is recommended:1. Use Table FLA
Multiply the NEC Table FLA value by 1.15.
2.
Consider Actual Current
If the motor has been previously operated and its actual current is known, use this value to calculate the overload size. However, be sure to consider any potential load changes or aging effects that may have altered the current draw.3.
Safety Factor
Always include a safety factor when sizing overloads to account for variables such as temperature, voltage fluctuations, and aging. A 15% safety factor is common.
Example Calculation
For a 5 horsepower, 460-volt, 1800 rpm motor with a missing nameplate, the estimated FLA using NEC Table 430.247 is 6.2 amps. Multiplying by a 15% safety factor gives an overload size of:
6.2 amps x 1.15 = 7.13 ampsTherefore, a motor overload with a setting of 7.13 amps would be appropriate. Flag for review