Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: detached garage grounding

User: Lefty0824, Location: New Jersey

Asked on: Saturday, March 26, 2011 at 1:19 pm EDT
Answered on: Tuesday, May 14, 2024 at 3:19 am EDT

Question: 100 amp main lug sub-panel in a detached garage am I required to drive a ground rod? I pulled an equipment grounding conductor with the phase conductors in the conduit.

Yes, you are required to drive a ground rod.

NEC 250.30(A)(3) states that a separate grounding electrode system shall be installed for detached buildings.The equipment grounding conductor (EGC) that you pulled with the phase conductors in the conduit is only for grounding the electrical system within the garage. It does not provide a path to earth for lightning or other fault currents.The ground rod provides a low-resistance path to earth for these currents and helps to protect people and equipment from electrical shock. Flag for review

Previous Question Next Question