User: sparky354, Location: Lockport, IL
Asked on: Tuesday, March 29, 2011 at 11:45 am EDT
Answered on: Tuesday, May 14, 2024 at 3:26 am EDT
Question: Is anyone aware of a code article requiring general purpose receptacles in an electrical room ? All I can find is the Illimination requirements of Art. 110.
NEC 2023450.11 Electrical Closets.(A) Receptacles. At least one receptacle outlet shall be provided in every electrical closet and shall be located not more than 1.8 m (6 ft) from the electrical equipment.Exception: A single receptacle outlet shall be provided for each combination of two or more adjacent electrical closets where they are interconnected by doorways, and where one receptacle is within 1.8 (6 ft) of each doorway. Flag for review