User: tankfarms, Location: Florida
Asked on: Wednesday, March 30, 2011 at 9:59 am EDT
Answered on: Tuesday, May 14, 2024 at 3:28 am EDT
Question: Hello,We have a motor that just went through a rewinding/VPI recently, and when it was installed back to service, the noise it?s making is quite louder (I want to say maybe 5 to 8 times more). This motor is used to drive a pump, and its specs are 450HP, FLA 108A, 2.4KV. Mechanical checked all vibrations found no issues and electrical also check the load, and everything is balanced. I thus wonder if the fact that the motor went through the rewind now caused some change inside the windings? Wonder what more can we check when the motor is in service. Any advice?
Possible Causes of Increased Noise after Rewind
Improper winding
Misalignment, uneven spacing, or poor insulation between turns can create magnetic imbalances and cause noise.
Uneven air gap
Differences in the distance between the stator and rotor can result in magnetic pull and increased noise.
Bearing issues
Rewinding may have affected the bearing alignment, lubrication, or condition.
Rotor balance
An unbalanced rotor can introduce vibrations that can amplify noise.
Resonance
Changes in the winding or other components may have shifted the motor's resonant frequency, making it more susceptible to noise.
Additional Checks in Service
Motor current harmonics
Use a power analyzer to measure current harmonics. Excessive harmonics can indicate winding issues.
Vibration analysis
Perform vibration measurements at various points on the motor to identify any abnormal vibration patterns.
Temperature monitoring
Check stator and bearing temperatures using infrared thermography. Excessive temperatures can indicate winding problems or bearing issues.
Magnetic field measurements
Use a gauss meter to measure the magnetic field around the motor. Uneven magnetic fields can indicate winding imbalances.
Power factor
Measure the motor's power factor. A low power factor can indicate certain types of winding issues.
Recommendations: Contact the rewind shop for their assessment and possible solutions. Perform a thorough visual inspection of the motor, paying attention to winding connections, insulation, and bearing condition. Consider performing a partial rewind to replace only the affected portion of the windings. Check the motor's mounting to ensure it's secure and not contributing to vibrations.* Consult with a motor expert for further troubleshooting and recommendations. Flag for review