Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Feeding another panel without feed through lugs..

User: jrobi030, Location: Chapel Hill, NC

Asked on: Thursday, March 31, 2011 at 10:58 am EDT
Answered on: Tuesday, May 14, 2024 at 3:33 am EDT

Question: Having a hard time finding this in the NEC. I have a standard 100A MLO panelboard. The incoming lugs have that panelboard's incoming feeders, as well as outgoing feeders to another panel attached. I am pretty sure the code does not allow this, but does anyone know the specific section? Note...these are not feed thru lugs...the standard incoming lugs have an incoming and outgoing set.Thanks!!!

NEC 408.3(D)Rule:

Panelboards shall not be used as junction boxes, raceways, or auxiliary gutters. A panelboard shall not supply more than one distribution system. Flag for review

Previous Question Next Question