Question: Having a hard time finding this in the NEC. I have a standard 100A MLO panelboard. The incoming lugs have that panelboard's incoming feeders, as well as outgoing feeders to another panel attached. I am pretty sure the code does not allow this, but does anyone know the specific section? Note...these are not feed thru lugs...the standard incoming lugs have an incoming and outgoing set.Thanks!!!
NEC 408.3(D)Rule:
Panelboards shall not be used as junction boxes, raceways, or auxiliary gutters. A panelboard shall not supply more than one distribution system. Flag for review