Topic: Phasing

User: Brandon Loyd, Location: 3 Hr 2 Min from Winged Horses

Asked on: Friday, April 1, 2011 at 11:58 am EDT
Answered on: Tuesday, May 14, 2024 at 3:37 am EDT

Question: Is it legel to use white or gray wire, if phase tape is installed, for line voltage conductors? #10 and #12.

Yes, in accordance with 2023 NEC 400.22(C).For line conductors over #8 AWG, at least one line conductor in a multiconductor cord set shall, so far as practicable, be continuously covered with white or gray insulation. Flag for review