Question: I know off an agency that wants to run 2 different branch curcuits through the same raceway. the branch circuits are fused conductors fed from 2 different transformers which are feeding 2 different lighting circuits. This seems so wrong. and you wonder why dogs and people are being shocked. I cant seem to find it in NEC. any clues
NEC Section 300.2: Use of Raceway for Multiple Circuits"Raceways shall not contain more than one circuit except as permitted in 300.3 or 300.5 through 300.
11."Exceptions
Section 300.3
Permits multiple circuits in the same raceway under certain conditions, such as when the raceway is large enough to accommodate all the conductors.
Sections 300.5 through 300.11
Provide specific exceptions for different types of circuits, such as remote-control, signaling, or power-limited circuits.
In this case
The scenario described in the question does not fall under any of the permitted exceptions. Therefore, running two different branch circuits through the same raceway from two different transformers would be a violation of NEC 300.2.
Reasons for the Requirement
Electrical Safety
Mixing circuits from different sources can create potential shock and fire hazards due to potential differences between the circuits.
Maintenance and Troubleshooting
Having multiple circuits in the same raceway can make it difficult to isolate and troubleshoot electrical issues.
Conductor Capacity
The raceway must have sufficient capacity to safely accommodate all the conductors and their associated insulation.
Possible Consequences
Electrical Shock
The presence of different voltages and currents in the same raceway can increase the risk of electrical shock to individuals working on or near the circuits.
Fire Hazard
Overloaded conductors or insulation damage can lead to overheating and potential fires.
Equipment Damage: Mixing circuits can interfere with the proper operation of equipment connected to the circuits. Flag for review