Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Machine Wiring

User: A/A Fuel GTX, Location: WI & AZ

Asked on: Monday, April 4, 2011 at 2:15 pm EDT
Answered on: Tuesday, May 14, 2024 at 3:44 am EDT

Question: I have a processing machine with numerous motors and electronics as part of the assembly. This particular machine has a FLA rating of 60A @ 208V, 3 Phase. Would I use 430.52 to size the OCPD and 430 Part II for sizing the conductors?

Yes, you would use 430.52 to size the OCPD and 430 Part II for sizing the conductors for this application.

OCPD Sizing (430.52)

The full-load amperes (FLA) of the machine is 60A. 430.52 requires sizing the OCPD at 125% of the FLA rating. Therefore, the OCPD size is: 60A 1.25 = 75A.

Conductor Sizing (430 Part II)

Part II of Article 430 provides tables for sizing conductors for motors. For a 3-phase motor operating at 208V, the table in 430.250 indicates the following minimum conductor sizes: Phase conductors: 4 AWG copper Neutral conductor (if required): 1/0 AWG copper

Note:
You may also need to consider other factors such as ambient temperature, wire type, and conduit fill when selecting the conductor size. It is recommended to consult with a qualified electrician or electrical engineer to ensure proper sizing and installation of the electrical system for this machine. Flag for review

Previous Question Next Question