Question: I am trying to find the correct calculation for 31kW Solar Panels in DC to amperage in 3-Phase 208VAC.Is this the correct formula?A=W/208 x 1.73whereas A = amps and W = wattsThank you in advance...
Incorrect Formula
The formula A = W/208 x 1.73 is incorrect for calculating the amperage in 3-Phase 208VAC for a given DC power of 31kW.
Correct Formula
The correct formula for calculating amperage in a 3-Phase system is:
A = W / (√3 V PF)where: A = amperage W = power in watts (31kW = 31,000W) √3 (square root of 3) ≈ 1.732 (for 3-Phase systems) V = voltage in volts (208V) PF = power factor (assumed to be 1.0 for unity power factor)Calculating AmperageA = 31,000 / (1.732 208 * 1.0)A ≈ 88.2 ampsTherefore, the amperage in a 3-Phase 208VAC system for 31kW of solar panels in DC is approximately 88.2 amps. Flag for review