Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: MLO service?

User: jrvazzer, Location: Massachusetts

Asked on: Thursday, April 7, 2011 at 4:26 pm EDT
Answered on: Tuesday, May 14, 2024 at 3:55 am EDT

Question: Our landlord is suppying a 3000A breaker for our service. The only issue is that our main board is 200feet away in a locked mech rm. Our electrician is claiming that our main board 3000A does not require a disconnect means if the landlords service breaker that is feeding our MDP has a lock out breaker. So in other words our MDP is a MLO. Can you help me varify this in the NEC.

NEC Article 408.30(A)"Where an overcurrent protective device is accessible to other than qualified persons and where the voltage between conductors exceeds 250 volts, means shall be provided to lock or tag such overcurrent protective device in the open position."NEC Article 705.12(E)"Where main disconnects are installed in buildings for connection to distribution systems having a nominal voltage greater than 250 volts, the main disconnect shall be suitable for use as service equipment and shall be provided with a marking of the maximum size of the disconnect that shall be installed in the building."Analysis

The question is whether the landlord's 3000A service breaker, which is located 200 feet away from the main distribution panel (MDP), can serve as the main disconnect for the MDP.1.

Overcurrent Protection

The landlord's 3000A service breaker meets the requirement of Article 408.30(A) for an accessible overcurrent protective device. It is accessible to other than qualified persons and the voltage between conductors exceeds 250 volts.
2.


Main Disconnect

The landlord's 3000A service breaker is installed near the service entrance and is suitable for use as service equipment, meeting the requirements of Article 705.12(E).
3.


Remote Control

Article 408.30(A) does not require a disconnect means for the MDP if the incoming service breaker can be locked out. In this case, the landlord's 3000A service breaker has a lock-out mechanism, which allows it to be safely locked in the open position.

Conclusion

Based on the analysis of the NEC, it is

permissible
to use the landlord's 3000A service breaker as the main disconnect for the MDP, provided that it is locked in the open position when servicing the MDP. This is because the service breaker meets the requirements for overcurrent protection and a main disconnect, and it can be locked out remotely to prevent accidental energization. Flag for review

Previous Question Next Question