Topic: Motor Conductors

User: volt101, Location: New Hampshire

Asked on: Tuesday, April 12, 2011 at 6:08 am EDT
Answered on: Tuesday, May 14, 2024 at 4:05 am EDT

Question: When selecting the ampacity of conductors fora single motor, the rules set in 430.22 apply. If after you multiply thefull-load current in the motor tables and the product comes out to a value thathas an asterisk next to the conductor?s size in Table 310.16 [Double asteriskin the 2011?s Table 310.15(B)(16)], does the small conductor rules apply? Example:Assuming all terminations are rated for 75?C - Can a 115-volt single phase ?horsepower motor be wired with 14 AWG, or does it need to have 12 AWGconductors to be code compliant?

12 AWG conductors are needed to be code compliant.The small conductor rules do not apply since the ampacity of the conductors fora single motor is governed by 430.22*. Flag for review