Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Field Bends

User: erickench, Location: Brooklyn, NY

Asked on: Wednesday, April 13, 2011 at 9:01 am EDT
Answered on: Tuesday, May 14, 2024 at 4:08 am EDT

Question: This PassBook is loaded with lousy question/answers. Here's another one.Where rubber-covered conductors are used in a conduit, the minimum radius of the curve of the inner edge of any field bend, in terms of the internal diameter of the conduit, shall not be less thanA. 4 timesB. 6 timesC. 8 timesD. 10 timesIs there any rule in the NEC that explains this?

Yes, there is a rule in the NEC that explains this.

NEC 358.30(B)(2) states that "Where rubber-covered conductors are used in a conduit, the minimum radius of the curve of the inner edge of any field bend shall not be less than eight times the internal diameter of the conduit."The answer is C. 8 times. Flag for review

Previous Question Next Question