Topic: ampacity

User: romex jockey101, Location: Tennessee

Asked on: Wednesday, April 13, 2011 at 2:11 pm EDT
Answered on: Thursday, May 23, 2024 at 6:19 pm EDT

Question: why is it if you go to table 310.16 allowable ampacity of insulated conductors and go under 90* for thhn it says that 14awg can take 25i 12awg 30i 10awg 40i at the bottom of the page it says*see240.4d were it states that 14 has to be fused at 15i etc...so how is it a hasard if you used 14awg on a 20 amp ocp i never have im just woundering

Table 310.16 provides the allowable ampacity of insulated conductors based on their size and type, assuming they are installed in a raceway or cable. However, Section 240.4(D) requires that overcurrent protection devices be selected to protect conductors from damage due to overcurrents. For 14 AWG THHN wire, the maximum overcurrent protection device that can be used is 15 amps, as specified in Table 240.4(D).Using a 20 amp overcurrent protection device on a 14 AWG THHN wire would violate Section 240.4(D) because the overcurrent protection device would not be able to protect the conductor from damage in the event of an overcurrent. This could result in the conductor overheating and potentially causing a fire.It is important to note that the allowable ampacity of a conductor is not the same as the maximum overcurrent protection device that can be used on that conductor. The allowable ampacity is the maximum current that the conductor can safely carry without overheating, while the maximum overcurrent protection device is the maximum current that the overcurrent protection device will allow to flow through the conductor before it trips.In general, it is always best to use the smallest overcurrent protection device that is allowed by the Code for the conductor size and type being used. This will help to ensure that the conductor is adequately protected from damage due to overcurrents. Flag for review

Previous Question Next Question