Question: Here's another question that doesn't make any sense:The maximum length of exposed flexible metallic conduit at terminal connections of motors installed in a cellar may not exceedA. 3 feetB. 4 feetC. 5 feetD. 6 feetAccording to NEC 348.30(A) Exception 2 the correct answer would be 'C' 5 feet. But the answer key gives 'D' 6 feet as the answer. That doesn't make sense. Anybody wish to comment on this?
The answer key is incorrect. According to NEC 348.30(A) Exception 2, the maximum length of exposed flexible metallic conduit at terminal connections of motors installed in a cellar is 5 feet. Flag for review