User: kingelectric, Location: Tennessee
Asked on: Monday, April 18, 2011 at 9:55 pm EDT
Answered on: Tuesday, May 14, 2024 at 4:21 am EDT
Question: 3-480v 30amp rooftop units with 3 # 10s and one common # 10 ground wire in a 1'' conduit ,the inspector said we could not do this. Any code violation here??
Code Violation
Yes, there is a code violation according to the National Electrical Code (NEC) 2020:
NEC 300.17(C) states that a conduit shall not contain more than 3 current-carrying conductors of the same circuit unless the conductors are entirely within a raceway that is accessible for removing all the conductors at any time.In this case, the conduit contains 4 current-carrying conductors (3 hot wires and 1 neutral wire) of the same circuit, which violates the code requirement.
NEC 300.19(A) also states that the number of conductors permitted in a raceway shall not be such that the cross-sectional area of the conductors exceeds 40% of the interior cross-sectional area of the raceway.In this case, the cross-sectional area of the conductors is likely to exceed 40% of the interior cross-sectional area of the 1" conduit, especially if the wires are large gauge (#10 AWG).
Consequences of Violation
The presence of excessive conductors in a conduit can: Obstruct the future removal or installation of wires Increase the risk of wire damage and electrical faults Hinder proper heat dissipation and create a fire hazard
Corrective Action:
To comply with the code, you must: Use a larger conduit (e.g., 1.25" or 1.5") to accommodate the 4 conductors.* Separate the hot wires and neutral wire into different conduits. Flag for review