Topic: Conduits and Propane Tanks

User: aec123, Location: Olathe, Kansas

Asked on: Tuesday, April 26, 2011 at 8:59 am EDT
Answered on: Tuesday, May 14, 2024 at 4:38 am EDT

Question: How far do conduits need to be located from Propane Tanks in Miami/Dade??

According to the Miami-Dade Electrical Code (2017), Chapter 10, Section 1006.9.1

Conduit Clearances from Propane Tanks

Conduit shall be installed not less than 3 feet vertically and 1 foot horizontally from the relief valve outlet on any LP-Gas container. Flag for review