Topic: working surface in front of service?

User: lmwolfwalker, Location: Rock Springs, WY

Asked on: Thursday, April 28, 2011 at 9:30 am EDT
Answered on: Tuesday, May 14, 2024 at 4:44 am EDT

Question: The local inspector gave a code violation on a service installed saying NEC dictates a flat working surface in front of the service. Where in the code book would I find this? Service is for a lift station and is on a short hill about four feet off the ground...

There is no requirement in the NEC for a flat working surface in front of the service. Flag for review