Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Service Sizing

User: aelectricalman, Location: KY

Asked on: Friday, April 29, 2011 at 5:15 pm EDT
Answered on: Tuesday, May 14, 2024 at 4:48 am EDT

Question: What factors are considered with sizing wire for an electrical service? What I mean by this is, if I have a 600amp service, why should I have to have all three legs of a wye system sized to be able to withstand 600amps, knowing the system will never have 600amps on any leg at any time. I did not respond to the inspector because I didnt know what to say at that point! This is a sanity check for my own good. Thanks again. Is there nothing to be said about a balanced system?

Factors Considered in Wire Sizing for an Electrical Service Load Current

The maximum current that the service will be expected to carry. This is typically determined by the total connected load, which includes all appliances, lighting, and other electrical devices.


Voltage Drop

The amount of voltage lost between the transformer and the service panel. This is influenced by wire length, wire size, and load current.

NEC Requirements

The National Electrical Code (NEC) provides minimum wire sizes based on load current and voltage drop requirements.


System Capacity

The maximum current that the electrical system can safely handle. This is typically determined by the transformer capacity and the wire size.

Protection Devices

The type and rating of circuit breakers or fuses used to protect the wire and equipment.

Why Three Legs Must Be Sized for 600 Amps in a 600 Amp Wye System


Despite the fact that only one leg of a wye system will ever have 600 amps of current, all three legs must be sized to withstand 600 amps for the following reasons:
Phase Rotation

The phase rotation of a wye system can change unexpectedly, causing any leg to become the "hot" leg with 600 amps of current.

Unbalanced Loads

Even though the system is balanced under normal operating conditions, unbalanced loads can occur, such as when one appliance draws significantly more current than the others. This can cause one leg to experience higher current than the other two.


Ground Faults

A ground fault on one leg can cause the current in the other two legs to increase significantly, potentially exceeding 600 amps.

Arc Faults

Arcing faults can create extremely high currents in all three legs of the system, exceeding the capacity of smaller wires.


NEC Requirements

The NEC requires that all conductors in a multi-phase service be sized to handle the maximum potential current on any phase.

Balanced Systems


While it is desirable to have a balanced system where the load is evenly distributed across all three phases, it is not always possible to guarantee this condition. Therefore, the NEC requires that all conductors in a multi-phase service be sized for the maximum potential current, regardless of the balance of the load. Flag for review

Previous Question Next Question