Topic: feeder circuit estimate

User: frank_inks, Location: Olathe, Kansas

Asked on: Saturday, April 30, 2011 at 4:30 pm EDT
Answered on: Tuesday, May 14, 2024 at 4:49 am EDT

Question: helo guyzi just want to ask for opinions about wiring a feeder circuit from the main electrical room to the buildings...uhmm on what type of conduit, conduit fill, method of embedding conduits underground through a manhole, and also on how to compute its voltage drop, with all possible factors to be considered...thanks in advance for ur ideas..

## Wiring a Feeder Circuit for Underground Distribution### Conduit Selection PVC or HDPE conduit

Durable, corrosion-resistant, and suitable for underground burial.


Diameter

Based on the number and size of conductors, conduit fill requirements, and bends.### Conduit Fill

NEC Article 310.15(B)(1)
: Maximum cable fill for any raceway is 40%. Adjust for ambient temperature

Increase fill percentage for higher temperatures.

Consider derating

Reduce allowable fill percentage for continuous load conditions.### Underground Conduit Installation


Trenching

Excavate trenches at least 24 inches deep and maintain proper slope for drainage.

Manholes

Install manholes at intervals for access, splicing, and pulling cables.


Conduits through manholes

Protect conduits with sleeves or other approved methods.

Bending

Bend conduits smoothly using approved methods to avoid kinks or damage.### Voltage Drop Calculation

Factors to Consider

Conductor length Conductor size Load current Power factor Ambient temperature Soil resistivity Conduit length factor

Formula

Voltage Drop = (2 × Conductor Length) × (Load Current) × (Conductor Resistance) × (Length Factor)


Conductor Resistance

Conductor Resistance = (Resistivity × Conductor Length) / Conductor Area


Length Factor

Based on conduit type, soil conditions, and conductor spacing.

Corrections for Temperature and Power Factor



Temperature

Adjust voltage drop by a factor from NEC Table B.310(A)(1)


Power Factor

Multiply voltage drop by the inverse of the power factor (e.g., for a power factor of 0.8, multiply by 1.25)

Example

Calculate the voltage drop for a 100-amp feeder circuit from the main electrical room to a building 100 feet away using #4 AWG conductors in a PVC conduit underground.

Data

Conductor length = 100 feet (x2 = 200 feet) Load current = 100 amps Conductor resistance (from wire table) = 0.25 ohms/1000 feet Length factor = 0.9 (from NEC Table B.310(A)(1)) Ambient temperature = 30°C Temperature correction factor = 1.11 (from NEC Table B.310(A)(1))

Voltage Drop

Voltage Drop = (2 × 200 feet) × 100 amps × 0.25 ohms/1000 feet × 0.9 × 1.11= 9.89 volts


Conclusion:


The calculated voltage drop is 9.89 volts. This value is within acceptable limits for a 100-amp feeder circuit. It is important to adhere to NEC requirements and industry best practices to ensure a safe and reliable electrical distribution system. Flag for review