Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 517 health care ques?

User: wireman1, Location: Fl

Asked on: Monday, May 2, 2011 at 10:19 am EDT
Answered on: Tuesday, May 14, 2024 at 4:52 am EDT

Question: the following electrical systems are used in a hospital normal power, alternate power[ genators ] ,critical care,life safety, and life support can any of the above be run in the same conduit or must all of them be run in seperate conduits ?

All of the above electrical systems must be run in separate conduits. Flag for review

Previous Question Next Question