User: Fred B, Location: Upstate, NY
Asked on: Sunday, May 30, 2021 at 5:41 pm EDT
Answered on: Thursday, June 20, 2024 at 11:20 am EDT
Question: If I up size conductors for voltage drop from POCO to first disconnect can the balance from first disconnect to branch circuit panels be sized to the amperage of the loads of the individual panels or must the upsized conductors carry thru to the branch circuit panels? For reason of VD running 2 parallel 500kcmil AL to 400A meter/disconnect can I run from the disco to the 2 interior breaker panels two sets of 250kcmil AL one set to each panel, under 25ft from meter/disconnect to the interior panels?
Voltage Drop Considerations
Voltage drop calculations should be performed over the entire circuit from the POCO (Power Company) to the branch circuit panels. Upsizing conductors for voltage drop from the POCO to the first disconnect is acceptable, as this will reduce the voltage drop over that section.
Conductors to Branch Circuit Panels
The circuit conductors extending from the first disconnect to the branch circuit panels must be sized to handle the total amperage of the loads within those panels. The amperage of the loads at each branch circuit panel can be summed to determine the required conductor size. It is not required to maintain the upsized conductor size throughout the entire circuit if the amperage of the loads decreases at each branch circuit panel.
Parallel Conductors
Running two parallel 500kcmil AL conductors to the 400A meter/disconnect is acceptable. The current-carrying capacity of the parallel conductors is equal to the sum of their individual capacities. If you intend to run two sets of 250kcmil AL conductors from the disconnect to the two interior breaker panels, ensure that each set of conductors is sized appropriately for the amperage of the loads in the respective panel.Based on your description, the following is a possible layout:
Meter/Disconnect
Two parallel 500kcmil AL conductors
Interior Panel 1
One set of two 250kcmil AL conductors (sized for the amperage of the loads in this panel)
Interior Panel 2
One set of two 250kcmil AL conductors (sized for the amperage of the loads in this panel)
Note: The maximum allowable distance for parallel conductors is 30 feet (9.14 meters).* You should consult local electrical codes and regulations for specific requirements in your area. Flag for review