Question: Please see attached sketch. I have High Rise that has 277/480V main service switchboard 2000A.The switchboard feeder has Bkr#1 Standby Load and second feeder has Bkr#2 to emergency life and safety load. Downstream has ATSs and emergency generator.As I read it emergency systems are Not allowed to be on Ground fault protection only detection is allowed NEC 2017 section 709.6(D)However NEC 2017 section 215.10 requires GFPE on feederIts confusing Questions:1. would GFPE be allowed on in swtichboard BKr#2 that feeds emergency load or Bkr #1 that feeds standby load attached sketch or not?2. Would GFPE be allowed at the generator breaker?
1. GFPE on Switchboard Breakers According to NEC 2017 Section 709.6(D), ground fault protection is not allowed for emergency systems, only detection. Emergency systems include: Life safety systems (e.g., fire alarms, emergency lighting, exit signs) Legally required standby systems (e.g., hospitals, data centers) Therefore, GFPE is not allowed on switchboard Breaker #2 that feeds the emergency load. GFPE is allowed on switchboard Breaker #1 that feeds the standby load, as it is not an emergency system.2. GFPE on Generator Breaker NEC 2017 Section 215.10 requires ground fault protection on feeders. However, NEC 2017 Section 709.6(D) states that ground fault protection is not allowed for emergency systems. In this case, the generator breaker feeds both the emergency load and the standby load. To comply with both NEC requirements, two generator breakers would be required: One breaker without GFPE for the emergency load One breaker with GFPE for the standby load Flag for review