User: Grouch, Location: New York, NY
Asked on: Monday, May 5, 2025 at 1:53 pm EDT
Answered on: Monday, May 5, 2025 at 1:54 pm EDT
Question: When running a load calculation to calculate a service or feeder size, I use the nameplate values whether I'm following the standard or optional calculations of Article 220.For example, I'll use the nameplate wattage of a hot water heater, listed at 240 volts.If I have, which I always do, a 208 volt service, where in the code does it state that I can downsize the branch breaker for the water heater due to connecting to a 208 volt supply? At 208 volts, the wattage of the water heater (rated at 240 volts) will be derated to 75%. And the current will be derated to about 86%.
You're touching on a very common and often misunderstood aspect of electrical installations. You're right that a 240V-rated appliance will draw less power and current when connected to a 208V supply. However, the NEC does not explicitly allow you to downsize the branch circuit breaker based solely on the voltage difference and the resulting lower wattage. Here's why, and where the relevant code sections apply
Why You Can't Automatically Downsize the Breaker:
Safety Factor
The NEC prioritizes safety. The nameplate rating of the appliance represents the maximum power it could draw under rated conditions. This accounts for manufacturing tolerances and potential variations.
Future Proofing
A 240V appliance might be moved to a 240V supply later. Wiring the branch circuit according to the nameplate keeps it compliant.
Operating Conditions
The appliance could still draw close to its nameplate wattage under certain conditions even on a 208V supply, like during initial startup or heavy use.
Relevant NEC Sections
Article 110.3(B) - Installation and Use
“Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.” This means you must follow the manufacturer's instructions. If the manufacturer explicitly states in the instructions that the appliance can be used on 208V with a specific circuit breaker size that's lower than what the nameplate wattage implies, then you can follow that.2.
Article 210.21(B) - Branch Circuits
(B) Overcurrent Protection. Overcurrent protection for branch circuits shall be provided as specified in (B)(1) through (B)(3). This section focuses on the overcurrent protection of the circuit, not necessarily the nameplate. It doesn't grant you permission to lower the breaker if not explicitly stated by the manufacturer.3.
Article 422 - Appliances
Specifically, look for any manufacturer's notes or instructions provided with the appliance regarding voltage variation. Some manufacturers may provide guidelines on adjusting breaker and conductor sizes for 208V operation, but this is rare.
How to Handle the 208V Situation (Practically)
Consult the Manufacturer
This is the most important step. Contact the appliance manufacturer (or refer to the installation manual). Ask them directly if they provide specific instructions or derating factors for 208V operation and the corresponding breaker size. A written statement from the manufacturer is best.2.
Nameplate is the Default
In the absence of explicit manufacturer instructions for 208V use, you must size the branch circuit (including the breaker) based on the nameplate rating. This means using the nameplate wattage to calculate the current (I = P/V) at the nameplate voltage (240V) and then selecting a breaker that's at least 125% of that calculated current.3.
Feeder/Service Calculations - Demand Factors and Diversity
While you can't typically reduce the branch circuit breaker size, the fact that appliances connected to a 208V system draw less power does affect the overall feeder/service load calculation. In this case, you can apply demand factors (if available) or diversity factors to your feeder calculation, which will account for the fact that all appliances rated at 240 Volts will draw less power at 208 Volts.
Example
Appliance
240V, 4500W water heater.
Calculation at 240V
Current = 4500W / 240V = 18.75A. Breaker size = 18.75A 1.25 = 23.43A. You would use a 25A breaker (next standard size).
Calculation at 208V (theoretical)
Wattage at 208V ≈ 3000W. Current at 208V ≈ 14.4A. However, you
cannot automatically use a 15A breaker.
Required Action
You must install a 25A breaker based on the nameplate unless the manufacturer explicitly allows a smaller breaker in their instructions.
In Summary:The NEC is designed for safety and assumes you'll follow the manufacturer's instructions. You generally cannot downsize the branch circuit breaker for a 240V appliance connected to 208V unless the manufacturer explicitly provides instructions and ratings for 208V operation. Always prioritize safety and consult the manufacturer. The lower load imposed by the lower voltage, however, can be factored into feeder/service load calculations. Flag for review