Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Rules for installing low voltage reactors

User: Tainted, Location: New York

Asked on: Saturday, May 10, 2025 at 11:40 pm EDT
Answered on: Tuesday, May 13, 2025 at 8:23 pm EDT

Question: What are the rules that govern installing low voltage reactors (less than 600V) for limiting fault current?All I could find is NEC article 470 sections 470.1, 470.2, 470.3, 470.4 and that's it...?must it these reactors be treated like in article 450? Are there any other rules outside of the NEC for installing the low voltage reactors?

You're right, Article 470 in the NEC is specifically dedicated to Reactors. The sections you mentioned (470.1 through 470.4) cover the scope, definitions, general requirements, and location of reactors.Let's break down what the NEC does and doesn't cover, and then look beyond the NEC

What the NEC Covers (Article 470):
470.1 Scope

This article covers the installation of reactors.


470.2 Definition

Defines what a "reactor" is.

470.3 General



(A) Open Reactors

Must be readily accessible for inspection and maintenance.

(B) Dry-Type Reactors

Must be mounted in accordance with the manufacturer's instructions.


(C) Oil-Filled Reactors

Must comply with Article 450 (Transformers).

This is key!
470.4 Location

Reactors must be readily accessible for inspection and maintenance unless isolated by enclosure or elevation.

What's Missing/Implied in the NEC (and where to find it)



Specific Conductor Sizing & Overcurrent Protection

Article 470 itself doesn't provide detailed rules for conductor sizing and overcurrent protection.

You must refer back to other articles in the NEC



Article 240 (Overcurrent Protection)

This is the primary article governing overcurrent protection. You'll need to determine the ampacity of the reactor's conductors and select appropriate overcurrent protection based on that ampacity and the type of conductor. Look at sections regarding conductor protection, protection of equipment, and specific device requirements (like fuses or circuit breakers).


Article 310 (Conductors for General Wiring)

This article dictates how to determine the ampacity of conductors. You'll need to consider factors like the conductor's insulation type, ambient temperature, number of conductors in a raceway, etc.

Article 400 (Flexible Cords and Cables)

if the reactors use Flexible Cords and Cables


Wiring Methods

The NEC doesn't explicitly state how to wire the reactor (e.g., conduit, cable tray, etc.). You'll need to comply with the articles covering wiring methods based on your specific installation.

Chapter 3 (Wiring Methods and Materials)

Choose the appropriate wiring method (e.g., rigid metal conduit, EMT, MC cable) based on the environment, voltage, and any specific requirements.


Grounding

Article 250 (Grounding and Bonding) is crucial for safety. You'll need to ensure the reactor's enclosure (if any) is properly grounded according to the NEC.

Why Article 450 is Important (Even for Low Voltage Reactors)



Oil-Filled Reactors

470.3(C) explicitly states that oil-filled reactors must comply with Article 450 (Transformers). This makes sense because oil-filled reactors share similar safety concerns with transformers (e.g., potential for leaks, fire hazards).


General Similarities

Even for dry-type reactors, you can often use Article 450 as a guideline for best practices. Consider these aspects:

Ventilation

Reactors, like transformers, generate heat. Ensure adequate ventilation to prevent overheating. See Article 450 for transformer ventilation requirements, and apply similar principles to reactors, adjusting for the reactor's specific heat dissipation characteristics.


Overcurrent Protection

While you must use Article 240 for overcurrent protection, Article 450 gives you additional insight into the types of protection commonly used for similar equipment.

Rules Outside of the NEC



Manufacturer's Instructions

The most important rule
outside of the NEC is the

manufacturer's installation instructions
. These instructions take precedence over general codes. The NEC often references or requires compliance with manufacturer instructions. Local Amendments to the NEC

Your local jurisdiction (city, county, state) may have amendments or additions to the NEC. Always check with your local electrical inspector to see if any specific rules apply in your area.

National Standards (Beyond the NEC)



IEEE Standards

Organizations like the Institute of Electrical and Electronics Engineers (IEEE) publish standards related to power systems and equipment. While not legally binding like the NEC, these standards provide valuable guidance on best practices and engineering considerations. Look for standards related to reactors, fault current limitation, and power quality.

NEMA Standards

The National Electrical Manufacturers Association (NEMA) publishes standards related to electrical equipment manufacturing and performance. These standards can help you understand the specifications and capabilities of different types of reactors.


Engineering Design Considerations



Fault Current Calculation

Accurately calculate available fault current
with and without the reactor. This is critical to selecting a reactor with the appropriate impedance to achieve the desired fault current reduction.

System Coordination Study

Perform a coordination study to ensure that overcurrent protective devices (OCPDs) are properly coordinated to minimize nuisance tripping and selectively clear faults. The addition of a reactor can affect coordination, so it's essential to re-evaluate the system after the reactor is installed.

Voltage Drop

Reactors introduce voltage drop. Calculate the expected voltage drop under normal and fault conditions to ensure it remains within acceptable limits.


Harmonic Distortion

Reactors can sometimes contribute to harmonic distortion in the electrical system. Consider the potential impact on harmonic levels and implement mitigation measures if necessary.*

Resonance

Reactance in a circuit can cause resonance at certain frequencies. Perform an analysis to ensure that the reactor does not create a resonance condition that could damage equipment or cause instability.

In Summary


NEC Article 470 is the starting point, but it's not the whole story.
2. Always follow the manufacturer's instructions.3. Refer to other NEC articles (240, 310, 250, Chapter 3) for conductor sizing, overcurrent protection, grounding, and wiring methods.4. Use Article 450 (Transformers) as a guideline for best practices, especially for oil-filled reactors and ventilation concerns.5. Check for local amendments to the NEC.6. Consider IEEE and NEMA standards for additional guidance.7. Perform thorough engineering design calculations and studies (fault current, coordination, voltage drop, harmonics, resonance).

By following these steps, you can ensure a safe and compliant installation of low-voltage reactors for limiting fault current. When in doubt, consult with a qualified electrical engineer. Flag for review

Previous Question View on the official Mike Holt Forum Next Question