Topic: Neutral Calculation for Balanced Inverter per NEC2023

User: MarcialMS, Location: Costa Rica

Asked on: Monday, May 12, 2025 at 6:16 pm EDT
Answered on: Tuesday, May 13, 2025 at 8:27 pm EDT

Question: Hi.How can I design the neutral conductor for a PV inverter according to NEC 2023?The inverter is a SMA Core 1, 62.5 kW-US. The manufacturer indicates that this inverter has less than 3% of THD.The phase conductors are going to be 1/0 AWG (because of voltage drop)Several colleagues indicate that balanced systems do not need the neutral, at all. Others than non lineal systems must be sized 100% of the phase conductors and a few told me to size the neutral as the EGC per 250.122.This should be ok for 1 inverter, but in my case, I must install 40 Core 1 in a single project. This means 40 x 100%-sized conductors represent a big part of the budget.I just need the correct Code reference to justify this to the inspector.Thanks in advance.

Okay, let's break down the neutral conductor sizing requirements for your SMA Core 1 PV inverters, considering NEC 2023 and the specific details of your project (40 inverters, THD less than 3%, and the opinions of your colleagues). This is a common area of confusion in PV design, and the NEC has undergone changes in recent editions.

Understanding the Basics (NEC 2023) General Rule (Article 220)

Article 220 contains the general rules for branch-circuit, feeder, and service calculations. You'll use this to
determine whether a neutral conductor is required and how to calculate its load.

Specific Equipment (Article 690)

Article 690, "Solar Photovoltaic (PV) Systems," supplements or modifies the general requirements of the NEC. Crucially, 690.8 specifically addresses circuit current and conductor sizing in PV systems.

Neutral Current Calculation (220.61)

This section is
essential. This section gives the procedure on how to size the neutral.

Harmonic Currents

Non-linear loads (those with significant harmonic distortion) can cause increased current flow in the neutral conductor.

Key Considerations for Your Situation
1. SMA Core 1 Inverter THD

The manufacturer's specification of "less than 3% THD" is extremely important. A low THD is very helpful in reducing the need for an oversized neutral.2.

Balanced vs. Unbalanced Loads

Balanced Loads (Ideal Case): In a perfectly balanced three-phase system (equal loads on each phase and no harmonic distortion), the neutral current theoretically would be zero. This is where the argument for omitting the neutral comes from. However, perfect balance is rarely achieved in the real world, especially with multiple inverters. Unbalanced Loads (Reality): Slight variations in inverter output, line impedances, and other factors will create some amount of imbalance. Harmonics further exacerbate this.3.

NEC Requirements and Interpretations



Neutral Conductor Required?

This is the first and most important question. Does the equipment (in this case, the inverters) require a neutral conductor for its operation? Consult the inverter manufacturer's installation manual and technical specifications. If the manufacturer requires a neutral for proper inverter operation, then you MUST provide it, regardless of whether you think it's needed based on load calculations.

If a Neutral is Required (or Provided)



220.61(C)(1)

In a 3-wire circuit consisting of two phase wires and a neutral from a 3-phase, 4-wire system, calculate the maximum neutral current as the maximum unbalanced load between the neutral and any one of the phase conductors.


220.61(C)(2)

In a 3-phase, 4-wire system, calculate the maximum neutral current as the square root of the sum of the squares of the maximum unbalanced load and the harmonic neutral current.4.

Equipment Grounding Conductor (EGC)

The neutral conductor and the EGC have fundamentally different functions. The neutral conductor carries the current resulting from unbalanced loads and harmonics, while the EGC provides a low-impedance path to ground for fault currents, enabling overcurrent protective devices (OCPDs) to trip quickly. Do not size the neutral based on the EGC requirements.

Step-by-Step Approach to Neutral Sizing (According to NEC 2023, considering your specific scenario)
1. Manufacturer Requirements

First and foremost, read the SMA Core 1 installation manual thoroughly. Look for explicit statements about the need for a neutral conductor. If SMA requires a neutral for proper operation or warranty compliance, your decision is made.2.

Calculate the Maximum Unbalanced Load (220.61(C)(1))

Determine the maximum current output per phase of each inverter. The spec sheet should give you this. Estimate the maximum difference in current between any two phases across all 40 inverters. This is the tricky part. Consider worst-case scenarios where some inverters are operating at maximum power while others are curtailed or shaded. This is where your engineering judgment comes in. Unless you have real-time monitoring data or a very specific reason to assume tight balance, you'll need to make a reasonable, conservative estimate. How unbalanced could the total system realistically be? This unbalanced load in amperes becomes a starting point for your neutral conductor ampacity.3.

Calculate the Harmonic Neutral Current (220.61(C)(2))

Use the 3% THD figure provided by SMA. Multiply the maximum phase current (from Step 2) by the THD value (0.03). This gives you the approximate harmonic current. For more conservative sizing of your neutral conductor, you can add 100% of the nonlinear load connected between any phase conductor and the neutral conductor. In this case, there are no loads connected between the phase and the neutral. This value will likely be very small given the low THD.4.

Determine the Neutral Conductor Ampacity (220.61)

Use the most conservative formula provided in 220.61: square root of the sum of the squares of the maximum unbalanced load and the harmonic neutral current. Select a neutral conductor size with an ampacity equal to or greater than the calculated value.5.

Adjustment Factors (310.15)

Apply any applicable ampacity adjustment factors from NEC 310.15 (temperature correction, conduit fill, etc.). These factors reduce the allowable ampacity of the conductor, so you may need to upsize.6.

Minimum Size (250.24(C))

Pay close attention to this! Even if your calculations result in a smaller size, the neutral conductor must be sized no smaller than what is specified in 250.24(C). In the case of multiple service disconnects, the size of the neutral should not be smaller than the minimum neutral conductor required for the largest service disconnect.

Justifying Your Design to the Inspector
Documentation is Key

Present a clear, step-by-step calculation showing how you arrived at your neutral conductor size, referencing the specific NEC sections you used (especially 220.61). Include the SMA Core 1 installation manual and the THD specification. Explain your assumptions about load imbalance and why you believe they are reasonable and conservative. Highlight the fact that you considered NEC 250.24(C) regarding minimum neutral size.

Be Prepared to Defend Your Assumptions

The inspector may question your estimates of load imbalance. Be ready to provide justification.


Consider a Load Study (If Possible)

If you have access to data from similar installations, a load study can provide valuable insights into real-world load imbalances and harmonics. This can strengthen your argument.

Communication

Talk to the inspector
before the installation, if possible. Discuss your design approach and address any concerns they may have. Early communication can prevent delays and costly rework.

Addressing Your Colleagues' Opinions
"Balanced Systems Don't Need a Neutral"

This is only true in a perfectly balanced system, which is unrealistic. The NEC provides for the possibility of imbalance.

"Size the Neutral 100% of the Phase Conductors"

This is often overly conservative,
especially with inverters that have low THD. The NEC allows for a reduced neutral size if the calculated neutral load is less than the phase conductor current. However, NEC 250.24(C) provides minimum requirements.

"Size the Neutral as the EGC per 250.122"

This is incorrect. The neutral and EGC have separate functions and are sized differently.

Example Calculation (Simplified)
Let's say the SMA Core 1 has a maximum output of 100A per phase. Assume a maximum imbalance of 20% across the 40 inverters (you would need to justify this). This means 20A. Harmonic current = 100A 0.03 = 3A Neutral ampacity (using the square root of the sum of the squares method): sqrt(20^2 + 3^2) = 20.22 AIn this simplified example, you might think a smaller conductor would suffice. However, you MUST check NEC 250.24(C) for the minimum allowed neutral size. It's highly likely that 250.24(C) will require a larger conductor than 20.22A.

Important Cautions
Local Amendments

Be aware of any local amendments to the NEC that may affect neutral sizing requirements.

Consult with an Engineer

If you are unsure about any aspect of the design or calculations, consult with a qualified electrical engineer.


AHJ Authority:
The Authority Having Jurisdiction (AHJ), typically the electrical inspector, has the final say on the interpretation and enforcement of the NEC.By following these steps and documenting your design decisions carefully, you can develop a safe and compliant neutral conductor sizing strategy for your PV inverter project. Good luck! Flag for review

Previous Question View on the official Mike Holt Forum Next Question