User: Elect117, Location: California
Asked on: Friday, May 30, 2025 at 12:40 pm EDT
Answered on: Friday, May 30, 2025 at 12:40 pm EDT
Question: I got sent prints to review and the designer is planning on feeding two panelboards off of one dry type.150kVA (480-208/120 3PH)250kcmil to 250 MCB600kcmil to 400A MCBI already noted that the secondary protection didn't meet Table 450.3(B) Note 2.But I didn't know if I needed to also mark the SBJ or GEC size for correction either. They have the SBJ and GEC sized at 1/0.My questions is, should they have sized the SBJ and GEC as 600kcmil + 250kcmil = 850kcmil => 2/0 or is it based on the largest single conductor from the transformer (600kcmil => 1/0)?If they needed 2/0, could you help point me to the section? Is it the "parallel" language that I am not interpretating right? I always thought parallel meant they started and ended at the same point like from chapter 310. The max current would be based on the largest conductor but do you need to consider them both faulting at the same time?
You are on the right track with your concerns. Let's break down the sizing requirements for the SBJ and GEC.
Understanding the Code Requirements Separately Derived System (SDS)
A transformer creating a new neutral point qualifies as an SDS.
Grounding Electrode Conductor (GEC)
Connects the grounding electrode system to the SDS.
System Bonding Jumper (SBJ)
Bonds the neutral point of the SDS to the transformer enclosure.
Key Code Sections
NEC 250.30(A)(1)
Sizing the Grounding Electrode Conductor (GEC) for a separately derived system. It states, "The size of the grounding electrode conductor for a separately derived system shall be based on the derived phase conductors and shall be in accordance with Table 250.66."
NEC 250.28(D)(1)
Sizing the System Bonding Jumper (SBJ) on the secondary side. It states, "For a grounded system, an unspliced system bonding jumper shall be used to connect the equipment grounding conductors and the service-equipment enclosure to the grounded conductor of the system... The size of the system bonding jumper for a separately derived system shall not be smaller than specified in 250.28(D)(1) through (D)(3) and shall be sized for the derived phase conductors."
Your Scenario
You have a 150kVA transformer with two sets of conductors coming from the secondary:1. 250 kcmil to a 250A MCB2. 600 kcmil to a 400A MCB
Analysis
The SBJ and GEC are sized based on the derived phase conductors. The code language specifically mentions that the sizing needs to be per conductor.
NEC 250.66 Table| Size of Largest Ungrounded Service-Entrance Conductor or Equivalent Area for Parallel Conductors | Size of Grounding Electrode Conductor
:--------------------------------------------------------------------------------------------- | :------------------------------------- |
Not over 1100 kcmil | 1/0 AWG |