Question: Not sure if PVC in an attic was a code violation. could not find anything in the building codes and might need to change some work. another contracter brought pvc into an attic space and the run was continued with more pvc instead of transitioning to emt.
Okay, let's break down the use of PVC conduit in attic spaces and whether it's a code violation.
Key Considerations
NEC (National Electrical Code)
The NEC is the primary electrical code in the United States, and most local codes are based on it. However, local jurisdictions can amend or add to the NEC, so you always need to check local codes first.
Mechanical Protection
One of the biggest concerns with PVC conduit is its lack of mechanical protection compared to EMT or rigid metal conduit. Attics can be subject to physical damage from various sources (storage, rodents, workers, etc.).
Temperature
Attics can experience extreme temperature swings, particularly high temperatures in the summer. This can affect the long-term durability and performance of PVC.
Wiring Method
The type of wiring within the conduit matters.
Support
All conduit, regardless of type, must be properly supported.
General NEC Guidance (Based on common interpretations and sections - always verify with the latest NEC edition and local amendments)
Chapter 3, Wiring Methods and Materials
This chapter covers the acceptable wiring methods, including conduits like PVC and EMT. Look specifically at the articles relevant to each conduit type.2.
NEC 352.12 (Uses Not Permitted)
This section of the NEC outlines specific situations where PVC conduit cannot be used. Common reasons:
Where subject to physical damage
If the attic space is likely to have objects stored or other physical damage, PVC may not be permitted.
Ambient Temperature
The PVC must be installed and used at temperatures that do not exceed the temperature listed on the product.3.
NEC 358.12 (Uses Not Permitted)
This section of the NEC outlines specific situations where EMT conduit cannot be used.
Specifically Regarding Attics
The NEC generally doesn't explicitly prohibit PVC in attics across the board. The permissibility comes down to the specific conditions of the attic and compliance with the general requirements for PVC and EMT conduit use. Physical Damage is Key
The main argument against PVC in an attic usually centers on the potential for physical damage. If the attic is used for storage, is likely to be accessed by workers who could step on or damage the conduit, or is prone to rodent activity, PVC may be deemed inappropriate unless it's adequately protected.
Temperature Considerations
Check the temperature rating of the PVC. If the attic regularly exceeds that temperature, it's a problem. Consider derating the ampacity of the conductors within the conduit if the ambient temperature is high.
Why the Other Contractor Transitioned to EMT (Possible Reasons)
Local Code Requirements
The jurisdiction might have a specific amendment to the NEC that requires EMT (or another metal conduit) in attics for physical protection. This is the most likely reason.
Inspector Preference/Interpretation
Sometimes, an electrical inspector might have a stricter interpretation of the "subject to physical damage" clause.
Best Practice/Conservative Approach
The contractor might have chosen EMT because they considered it a more robust and reliable wiring method for the attic environment, even if not strictly required by code.
Future Proofing
The contractor may have been aware of planned uses for the attic space that would create increased risk of physical damage.
Fire Rating
EMT might have been chosen to maintain a fire rating within the attic if the PVC was not rated for such conditions.
Steps to Take
Check Local Codes
This is the most important step. Contact your local building department or electrical inspector and ask specifically about the requirements for conduit in attic spaces. Inquire if they have any amendments or interpretations of the NEC that apply.2.
Assess the Attic Environment
Will the attic be used for storage? Is there a risk of physical damage to the conduit? What are the typical temperature ranges in the attic?3.
Review the PVC Installation
Is the PVC properly supported? Is the wiring method within the conduit appropriate for the application? Are the fittings and connections properly made?4.
Document Everything
Keep records of your communications with the building department, your assessment of the attic, and the details of the PVC installation.5.
Be Prepared to Make Changes
If the local code or the inspector requires it, you'll need to modify the installation.
In summary: PVC in attics is not inherently a code violation under the NEC, but it is frequently restricted or disallowed due to concerns about physical damage and local code amendments. You must* check local codes and the specific conditions of the attic to determine if the installation is compliant. If you are not sure, it is always a good idea to upgrade to EMT. Flag for review