Question: When you do a vd calc and you have either 120/208 or 277/480 how do you know which voltage to input. e.g. 277/480 which would it be?
Okay, let's break down how to choose the correct voltage for a voltage drop calculation when dealing with 120/208V or 277/480V systems. The choice depends on the load you are supplying and the wiring configuration.
Understanding the System Voltages 120/208V System
This is a 3-phase, 4-wire wye system.
208V is the phase-to-phase voltage (voltage between any two of the three phases). 120V is the phase-to-neutral voltage (voltage between any phase and the neutral conductor). 277/480V System
This is also a 3-phase, 4-wire wye system.
480V is the phase-to-phase voltage. 277V is the phase-to-neutral voltage.
Key Rule: Match the Voltage to the Load's Voltage
The most important principle is to use the voltage that directly supplies the load.
Here's a breakdown of when to use each voltage
Using 120V or 277V (Phase-to-Neutral)
If your load is a
single-phase load connected between one phase and neutral, you use the phase-to-neutral voltage (120V or 277V). Examples
Lighting circuits with 277V ballasts (in a 277/480V system) Standard 120V receptacles and lights (in a 120/208V system). Single-phase motors rated for 120V or 277V (connected phase to neutral).
Using 208V or 480V (Phase-to-Phase)
If your load is a
single-phase load connected between two phases you use the phase-to-phase voltage (208V or 480V) Examples
Electric heaters or other loads specifically designed to run on 208V, connected between two phases of a 120/208V system. Electric heaters or other loads specifically designed to run on 480V, connected between two phases of a 277/480V system. If your load is a
three-phase load (like a 3-phase motor), you use the phase-to-phase voltage (208V or 480V). Three-phase motors are almost always connected to all three phases.
Summary Table| System Voltage | Load Type | Voltage to Use
:-------------- | :------------------------------------ | :------------- |
120/208V | Single-phase (phase-to-phase) | 208V |
277/480V | Single-phase (phase-to-neutral) | 277V |