User: timm333, Location: Minneapolis, MN
Asked on: Thursday, June 5, 2025 at 3:07 pm EDT
Answered on: Thursday, June 5, 2025 at 3:07 pm EDT
Question: Just want to ask: is there some North American standard which addresses the “commissioning” of electric motor in a process plant. I know NETA-ATS is for testing/pre-commissioning. But I am looking for some standard which addresses the commissioning of motor under actual load conditions, where load on motor changes with process variables like fluid pressure and flow rate. Thanks.
You're right, NETA-ATS primarily focuses on acceptance testing and pre-commissioning, not dynamic commissioning under actual load conditions with varying process variables.Finding a single, universally accepted "North American standard" specifically dedicated to the commissioning of electric motors under actual load conditions with process variable changes is challenging. This is because commissioning, especially dynamic commissioning, is often highly process-specific and depends heavily on the equipment the motor is driving.However, here's a breakdown of relevant standards, resources, and best practices you can draw upon to develop a comprehensive commissioning plan for your application
1. Relevant Standards & Organizations (General Guidance):
ANSI/ISA-88 (Batch Control)
While not solely focused on motors, ISA-88 provides a framework for batch process control that can be applied to define operational states and transitions, which directly influence motor loading. Understanding the process states and how they impact the motor is crucial for effective commissioning.
IEEE Standards
IEEE doesn't have a single commissioning standard for motors, but several standards related to motor operation, protection, and testing are relevant. Consider IEEE 519 (Harmonic Control), IEEE 141 (Recommended Practice for Electric Power Distribution for Industrial Plants), and IEEE 112 (Standard Test Procedure for Polyphase Induction Motors and Generators) for understanding motor characteristics and performance.
NFPA 70E (Electrical Safety in the Workplace)
Ensures safe work practices during commissioning, especially when working with energized equipment under load.
2. Best Practices and Guidelines (More Practical Focus)
Equipment Manufacturer Recommendations
This is crucial. The motor manufacturer, the pump manufacturer (if driving a pump), and the overall system integrator (if applicable) will have specific commissioning procedures and recommendations. These should be your starting point. Follow their instructions diligently.
Process Control System Documentation
Your Distributed Control System (DCS) or Programmable Logic Controller (PLC) documentation is critical. It defines the control logic that governs the motor's operation based on process variables. Review this to understand how the motor should behave under different conditions.
Industry-Specific Guidelines
Depending on your industry (e.g., water/wastewater, chemical processing, oil & gas), there might be industry-specific commissioning guidelines or best practices related to motors and their driven equipment. Look for resources from relevant professional organizations.
Experienced Personnel
Engage experienced commissioning engineers or technicians who have a deep understanding of both electrical motor operation and the process control system. Their expertise is invaluable for developing and executing a successful commissioning plan.
3. Key Commissioning Steps for Motors Under Variable Load
Here's a structured approach to commissioning, focusing on dynamic load conditions:
Pre-Commissioning (Building upon NETA-ATS)
Complete all NETA-ATS testing and verification. Verify motor nameplate data against design specifications. Confirm proper motor mounting, alignment, and lubrication. Check electrical connections, wiring, and grounding. Perform motor insulation resistance (Megger) testing. Verify proper operation of motor protection devices (overloads, short-circuit protection). Bump test the motor to verify correct rotation.
Static Commissioning
With the motor disconnected from the load: Verify control signals from the DCS/PLC reach the motor starter/drive. Confirm proper operation of the motor starter/drive (e.g., soft starter, VFD). With the motor connected to the load, but the process offline (e.g., pump not pumping fluid, conveyor belt empty): Jog the motor to verify proper load connection and mechanical operation. Check for unusual noise, vibration, or heating.
Dynamic Commissioning (Under Load)
This is where the process variables come into play.
Define Operating Scenarios
Identify a range of operating scenarios that represent the expected process conditions (e.g., low flow, normal flow, high flow, pressure spikes, start-up, shutdown).
Develop Test Procedures for Each Scenario
Create detailed test procedures for each operating scenario. These procedures should specify: Target process variable values (e.g., flow rate, pressure). Expected motor operating parameters (e.g., current, voltage, speed, power factor). Acceptable tolerance ranges for these parameters. Steps to take if the motor performance deviates from expectations.
Monitor Motor Performance
Use appropriate instrumentation to monitor motor performance during each scenario. This may include: Ammeters and voltmeters. Power meters (kW, kVAR, power factor). Vibration analyzers. Thermocouples or RTDs to monitor motor winding temperature. Oscilloscopes to capture transient events.
Record Data
Meticulously record all data collected during commissioning. This data will be invaluable for troubleshooting and future performance monitoring.
Analyze Data and Adjust Control Parameters
Compare the measured motor performance to the expected performance. If necessary, adjust control parameters in the DCS/PLC or motor drive to optimize motor operation and ensure that it meets the process requirements. This may involve tuning PID loops or adjusting VFD parameters.
Verify Protection Settings
Ensure that the motor protection devices are properly set to protect the motor under all operating conditions. This may require adjusting overload relay settings or short-circuit protection thresholds based on the measured motor currents.
Repeat Testing
Repeat the tests for each operating scenario to verify that the adjustments have been effective.
Specific Points to Consider During Dynamic Commissioning
Motor Starting
Pay close attention to motor starting characteristics, especially with variable frequency drives (VFDs). Ensure that the VFD is programmed to provide adequate starting torque without exceeding the motor's thermal limits. Monitor starting current and acceleration time.
Harmonic Distortion
If using VFDs, be aware of potential harmonic distortion. Measure total harmonic distortion (THD) and take steps to mitigate excessive harmonics if necessary (e.g., using line reactors or harmonic filters).
Motor Cooling
Ensure that the motor is adequately cooled under all operating conditions. Monitor motor winding temperature and check for proper ventilation.
Variable Speed Operation (VFDs)
When commissioning motors with VFDs, pay attention to the following:
Speed Range
Verify that the motor can operate reliably over the required speed range.
Torque Capability
Ensure that the VFD can provide adequate torque at all speeds.
Regenerative Braking
If the application requires regenerative braking, verify that the braking resistor is properly sized and functioning correctly.*
Process Interlocks
Verify the operation of all process interlocks that affect motor operation. These interlocks are designed to protect the motor, the driven equipment, and the overall process.
In summary: There's no single standard that dictates the exact steps for dynamic commissioning of electric motors in a process plant. However, combining manufacturer recommendations, relevant IEEE standards (especially those related to motor testing and operation), and a structured approach like the one outlined above will help you develop a robust and effective commissioning plan. The key is to thoroughly understand the process, the motor characteristics, and the control system, and to monitor motor performance under a range of operating conditions. Flag for review