User: mltech, Location: Ft. Lauderdale
Asked on: Tuesday, June 10, 2025 at 6:13 pm EDT
Answered on: Tuesday, June 10, 2025 at 6:22 pm EDT
Question: Went to check on a condo pool equipment room as the chemical pumps (120v) were not functioning properly. After checking voltage and finding a back feed decided I better start unwiring some things and isolate the circuit. Found 2 conductors under ground that had burnt and were completely separated. They were conductive through the water in the conduit, enough to make a reading on my meter and also back feed on the next conductor. Pulled new circuits wired everything up turned it on and the pumps failed to work. Turned the circuit off and got whacked by the neutral?Turns out the previous, so called electrician, failed to bond the XO terminal on the transformer. I’m really glad I found the real problem as i keep thinking this could have been a devastating event…Now I want to rewire the whole room.
Wow, that's a textbook example of why proper grounding and bonding are critical, and it sounds like you caught a potentially dangerous situation just in time. The unbonded transformer XO is the smoking gun, and your instinct to rewire the room is absolutely the right call. Here's a breakdown of what likely happened, and a plan for rewiring the pool equipment room to bring it up to code and ensure safety
What likely happened:
Unbonded Transformer XO
This is the root of the problem. The XO terminal on a transformer provides the reference point for the neutral/grounded conductor. Without it being properly bonded (connected to the grounding electrode system), the potential of the neutral can float to dangerous levels relative to ground.
Faulty Conductors & Backfeed
The deteriorated conductors in the conduit were causing a current path through the water. This is enough to create the backfeed you were seeing.
Voltage on the Neutral
When you broke the circuit and got shocked, this indicates that the unbonded neutral was carrying voltage relative to ground. This voltage could be coming from an imbalance in the loads connected to the transformer, or from a fault somewhere else in the system.
Pump Failure
The voltage fluctuations and unstable neutral caused by the unbonded transformer likely damaged the pumps, or prevented them from operating correctly.
Corrosion
Pool equipment is highly susceptible to corrosion due to the chemicals and moisture present. Using wrong material for the environment will cause failures like this one.
Rewiring Plan
Disconnect Power
Shut off the main breaker feeding the transformer and the pool equipment room. Verify with a meter that the power is off on all circuits. Lockout/Tagout procedures are essential.2.
Inspect and Document
Before you start ripping things apart, thoroughly document the existing wiring. Take pictures, make notes on wire sizes, conduit runs, and how everything is connected (or was connected). This will be invaluable for troubleshooting.3.
Transformer Bonding (Priority #1)
Verify the Transformer
Confirm the transformer's KVA rating, primary and secondary voltages, and any other relevant specifications.
Bonding Conductor
Install a proper-sized bonding conductor (typically copper) from the transformer's XO terminal to the main grounding electrode system (GES) of the building. The size of this conductor is determined by the transformer's KVA rating (refer to NEC 250.30).
Grounding Electrode System
Ensure the GES is adequate and in good condition. This typically includes a grounding electrode conductor to a ground rod, water pipe, or other approved grounding electrode.
Clean and Tight Connections
Use appropriate connectors and ensure all connections are clean, tight, and corrosion-resistant. Apply anti-oxidant compound to aluminum connections.4.
Conduit and Wiring
Replace Everything
Given the condition of the existing wiring, it's best to replace all conduit, conductors, and junction boxes in the pool equipment room.
Conduit Type
Use rigid PVC conduit (Schedule 80 for direct burial) or stainless steel for above ground runs, as these are resistant to corrosion from pool chemicals. Do not use EMT or other ferrous metal conduit in this environment.
Conductor Type
Use THHN/THWN-2 conductors rated for wet locations.
Wire Sizing
Size the conductors appropriately for the load of the pumps and any other equipment, considering voltage drop. Use the appropriate ampacity tables in the NEC.
Separate Equipment Grounding Conductor (EGC)
Run a dedicated equipment grounding conductor (EGC) in each circuit to provide a low-impedance path for fault current back to the source. Do not rely on the conduit as the sole EGC. Size the EGC according to NEC Table 250.122, based on the overcurrent protection device size.
5.
GFCI Protection
Ground Fault Circuit Interrupters
All 120V receptacles and circuits serving pool equipment must be GFCI-protected. Install GFCI breakers in the panel or GFCI receptacles where needed.6.
Bonding of Metal Parts
Pool Bonding Grid
The NEC requires a bonding grid that interconnects all metallic parts within the pool area, including the pool structure itself, metal light fixtures, ladders, handrails, pump housings, and any other metallic components within 5 feet of the pool. This bonding grid helps to equalize the potential and minimize the risk of shock. Use solid copper bonding conductors, sized according to NEC Article 680.
Bonding Jumpers
Use bonding jumpers to connect metal conduits, enclosures, and equipment.7.
Overcurrent Protection
Circuit Breakers
Install appropriately sized circuit breakers to protect each circuit. Use HACR-rated breakers for motor loads.
Motor Protection
Consider adding separate motor overloads for the pumps to provide better protection against overheating and damage.8.
Disconnect Switches
Service Disconnect
Install a readily accessible service disconnect switch for the pool equipment room.
Equipment Disconnects
Consider installing individual disconnect switches for each pump to allow for safe servicing.9.
Wiring Practices
Waterproof Connections
Use waterproof connectors and fittings in all junction boxes and enclosures to prevent moisture from entering.
Proper Terminations
Torque all terminations to the manufacturer's specifications. Loose connections are a common cause of problems.
Labeling
Clearly label all circuits, breakers, and equipment.
Conduit Support
Properly support all conduit runs to prevent stress and strain on the wiring.10.
Inspection and Testing
Professional Inspection
Before energizing the system, have a qualified electrical inspector review the work to ensure it complies with all applicable codes and regulations.
Testing
Perform the following tests:
Ground Resistance Test
Measure the resistance of the grounding electrode system to ensure it is within acceptable limits (typically 25 ohms or less).
Continuity Testing
Verify the continuity of all grounding conductors.
Insulation Resistance Test (Megger)
Test the insulation resistance of all conductors to ensure there are no shorts or grounds.
Voltage Drop Test
Measure the voltage drop under load to ensure it is within acceptable limits.
GFCI Testing
Verify that all GFCI devices are functioning correctly.
Polarity Testing
Confirm correct polarity of all receptacles and circuits.
Safety Considerations
De-energize Completely
Never work on electrical equipment without first de-energizing the circuit and verifying it is dead with a meter.
Lockout/Tagout
Use proper Lockout/Tagout procedures to prevent accidental re-energization of the circuit.
Personal Protective Equipment (PPE)
Wear appropriate PPE, including safety glasses, gloves, and insulated tools.
Qualified Electrician
This type of work should only be performed by a qualified and licensed electrician.
Code References (NEC)
Article 250
Grounding and Bonding
Article 680
Swimming Pools, Fountains, and Similar Installations
Article 430
Motors, Motor Circuits, and Controllers*
Article 300
Wiring Methods
In summary: The unbonded transformer XO created a dangerous and unstable electrical system. Rewiring the pool equipment room with a focus on proper grounding, bonding, GFCI protection, and corrosion-resistant materials is the only way to ensure the safety and reliability of the equipment. Do not take shortcuts. Hire a qualified electrician who understands pool wiring and NEC requirements. Your diligence in spotting this and your commitment to fixing it right could very well prevent a serious accident. Flag for review