Topic: Additional Disconnect Switch for Automatic Transfer Switch

User: knorthouse, Location: USA

Asked on: Tuesday, July 1, 2025 at 3:06 pm EDT
Answered on: Tuesday, July 1, 2025 at 3:06 pm EDT

Question: This request involves the Electrical supply system for a future gas compressor station. The station will be supplied from a customer-owned, pad mounted transformer (167 KVA 8320GY/4800 120/240 1PH). The Transformer has a Primary bayonet fuse for Overcurrent Protection. Primary Utility metering will be used, with a pad mounted disconnect switch (Service Point) located between the Utility meter and the Transformer Primary. The meter will be mounted on a Utility pole that's several hundred feet away from the Transformer, and the pad mounted Service Disconnect switch will located near the meter.An Automatic Transfer Switch (800A) will be fed from the Transformer Secondary and from a standbye generator (80KW with 400A CB). The Transfer Switch and Generator will be mounted near the Transformer. My understanding of the NEC is that since there will be a disconnect switch (Service Point) located before the Transformer, the Automatic Transfer Switch isn't required to be Service rated, and so an additional Disconect switch before the Automatic Transfer Switch isn't required. Note that the output of the Transfer Switch feeds an Electrical building where an MCC with an incoming 800A 120/240 1PH CB for Feeder protection will be located. The Electrical Building will be located approx 300-400' from the Transformer/Gen/ATS location.I'd appreciate some experience-based advice on whether or not, even though not required, it would be a good idea to include an additional Disconnect Switch (800A 120/240V 1PH) between the Transformer Secondary and the Automatic Transfer Switch. The pad mounted Service Disconnect switch is medium voltage (8000V), and will be located quite far from the Transformer/Gen/ATS location (several hundred feet). The operators also may not have extensive experience working with medium voltage electrical equipment, which might make working instead with a low voltage Disconnect Switch mounted close by, safer and easier to isolate the Transfer Switch and downstream equipment.There is a cost consideration, but safety and ease of use may override that in this case. Your comments would be appreciated. Thank You.

Okay, let's break down this electrical setup and analyze the considerations for an additional disconnect switch. Your assessment of the NEC requirements is accurate. Since you have a service disconnect switch (the pad-mounted switch before the transformer), the ATS is technically not required to be service-rated, and another disconnect before it isn't strictly required.However, your instincts about safety and ease of operation are spot-on. Here's a more detailed analysis and my advice

Arguments For Adding a Disconnect Switch Between the Transformer Secondary and the ATS:
Enhanced Safety

This is the biggest driver. Working on 4800V equipment hundreds of feet away is far more dangerous than working on 120/240V equipment nearby. Having a readily accessible, low-voltage disconnect right next to the ATS and generator provides a much safer and more convenient way to isolate the ATS, generator, and downstream equipment during maintenance, troubleshooting, or emergencies. The primary disconnect requires trained personnel and potentially specialized equipment for safe operation.


Ease of Maintenance and Troubleshooting

Imagine you need to troubleshoot the ATS, generator, or anything downstream in the electrical building. Having to walk several hundred feet to operate a medium voltage disconnect, possibly in adverse weather, is inefficient and time-consuming. A local disconnect allows quick and easy isolation.

Operator Familiarity

You've already identified that operators might be more comfortable and familiar with low-voltage equipment. This reduces the risk of human error and promotes safer operations. Less reliance on specialized personnel is also a benefit.


Future Flexibility and Expansion

While not immediate, a disconnect offers flexibility for future modifications or additions to the system. It provides a clear point of isolation for any upstream or downstream work.

Reduced Arc Flash Hazard

While not completely eliminated, isolating the low-voltage side with a disconnect reduces the potential arc flash hazard when working on the ATS, generator, or electrical building. While proper PPE is always required, minimizing the potential hazard is always beneficial.


Code Compliance in Certain Circumstances

While your basic understanding of the code requirements is correct, there may be local or project-specific requirements that call for disconnects to be present, or located closer to specific equipment. Check your specific local code requirements to ensure all standards are being followed.

Arguments Against Adding a Disconnect Switch



Cost

An 800A 120/240V disconnect switch, enclosure, and associated labor will add to the overall project cost.


Space

Requires additional pad space near the transformer/generator/ATS location.

Increased Complexity

Adds another piece of equipment to the system, potentially increasing the probability of failure (though a well-maintained disconnect switch is very reliable).

My Recommendation: Include the Disconnect Switch.


Given your concerns about safety, ease of use, and operator experience, I strongly recommend including an 800A 120/240V disconnect switch between the transformer secondary and the ATS. The increased cost is a reasonable investment in the long-term safety and operational efficiency of the gas compressor station. The convenience and confidence it provides during maintenance and emergencies far outweigh the additional expense.

Key Considerations for Implementation



Disconnect Switch Type

Choose a robust, reliable disconnect switch suitable for outdoor use and the expected load conditions. A fusible disconnect offers an additional layer of protection.

Enclosure

Ensure the enclosure is weatherproof and properly sized to accommodate the disconnect switch and associated wiring.


Location

Place the disconnect switch in a readily accessible location, close to the ATS and generator, and away from potential hazards (e.g., vehicular traffic). Consider ergonomics – can operators easily reach the handle?

Clear Labeling

Clearly label the disconnect switch with its function and the equipment it isolates.


Grounding

Ensure proper grounding of the disconnect switch and enclosure.

Coordination

Properly coordinate the overcurrent protection devices (bayonet fuse, disconnect switch fuses (if applicable), generator circuit breaker, and MCC circuit breaker) to ensure selective tripping.


Documentation

Update all electrical drawings and documentation to reflect the addition of the disconnect switch.*

Training

Provide operators with thorough training on the operation and maintenance of the disconnect switch.

In Summary:


While not strictly required by code in your described configuration, adding a disconnect switch between the transformer secondary and the ATS is a prudent decision that significantly enhances safety, simplifies maintenance, and improves the overall operability of the gas compressor station. Prioritizing safety and ease of use, especially with operators who may not be highly experienced with high-voltage equipment, is a wise choice. Carefully consider the implementation details outlined above to ensure the disconnect switch is properly selected, installed, and maintained. Flag for review