Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 60 amp GFCI required vs recommended

User: crtemp, Location: Wa state

Asked on: Thursday, July 17, 2025 at 4:26 pm EDT
Answered on: Thursday, July 17, 2025 at 4:27 pm EDT

Question: I have a hot tub that has a nameplate rating of 48 amps but in the instructions it says that a 60 amp breaker is "recommended". Would this be a requirement as it doesn't say it is required?

You're right to be questioning this. Here's the breakdown: Nameplate Rating (48 amps)

This is the

absolute maximum continuous current
the hot tub
should draw under normal operating conditions. This is the critical number for safety. Recommendation (60 amp breaker)

The manufacturer recommends a 60 amp breaker. This is likely for a few reasons:

Startup Surges

Hot tubs, especially when first turned on or when heaters cycle on, can draw significantly more current than their continuous rating for a brief period. The larger breaker is designed to handle these surges without tripping.


Safety Margin

Manufacturers often build in a safety margin to reduce the risk of nuisance tripping.

Code Compliance

The National Electrical Code (NEC) often requires overcurrent protection to be sized based on a certain percentage
above the connected load (in some cases 125% of the continuous load for certain types of loads, which would push you close to 60 amps).

Here's what you MUST consider


Local Electrical Code

Your local electrical code is the law. It may have specific requirements for hot tub circuits that supersede the manufacturer's recommendation. Contact your local building department or a licensed electrician to confirm.2.

NEC (National Electrical Code)

Even if your local code doesn't explicitly address it, the NEC provides the basis for safe electrical installations. NEC Article 680 (Swimming Pools, Fountains, and Similar Installations) has sections that apply to hot tubs.3.

Wire Size

The wire gauge (thickness) used to connect the hot tub

must
be rated to handle the breaker's amperage. A 60 amp breaker requires thicker wire than a 50 amp breaker. Important: If you use a 60 amp breaker, the wiring to the hot tub MUST be sized for 60 amps, even if the nameplate says 48 amps. For example, according to NEC, you would typically need at least #6 AWG copper wire for a 60 amp circuit.

In summary

A 48-amp load needs protection against overcurrent, and the recommendation from the manufacturer to use a 60-amp breaker is given for a reason. It is highly likely that a 60 amp breaker is required to comply with the NEC and your local electrical codes. This is because of the continuous load requirements, potential surge loads, and safety margin considerations.

Consult a Licensed Electrician

The

best and safest
course of action is to consult a licensed electrician. They can: Review the manufacturer's instructions and local codes. Calculate the actual load requirements. Determine the appropriate breaker size and wire gauge.* Ensure the installation is safe and code-compliant.

Important Warning: Using a breaker that is too small (e.g., a 50 amp breaker) could lead to nuisance tripping, but it could also prevent your hot tub from operating properly. Using a breaker that is too large compared to the wire size (e.g., 60 amp breaker with wiring only rated for 50 amps) can create a serious fire hazard. It's vital to get this right. Flag for review

Previous Question View on the official Mike Holt Forum Next Question