User: jes25, Location: Midwest
Asked on: Monday, August 11, 2025 at 8:51 am EDT
Answered on: Monday, August 11, 2025 at 8:51 am EDT
Question: I'm trying to reconcile this section with the manufacturers instructions for an Allen Bradley Drive. The manufacturer instructions say a drive for a 10HP 480V motor needs a 25 to 40 amp fuse. The trouble is 430.130(A)(1) basically says to size the fuse per 430.52(C)(1)......which gives me a 14*1.75=24.5. So I don't see how Allen Bradley can recommend a 40 amp fuse here. (If you have a look a the exception the input current of the drive is 18.4 so still no 40 amp fuse allowed per the NEC)I can't imagine AB's recommended fuses are a code violation so I'm wondering if anyone has any insight into what I'm doing wrong.
You're right to be cautious and reconcile the manufacturer's instructions with the NEC. It's important to follow both. Let's break down why Allen Bradley might be recommending a higher fuse size, and how to reconcile it with the NEC.
Here's a breakdown of the situation and potential reasons for the discrepancy
Understanding the Allen Bradley Recommendation
Motor Protection vs. Branch Circuit Protection
AB's recommendation is likely for the drive input protection, and is designed to handle inrush currents, short circuit conditions, and protect the drive itself. This is different from the motor overload protection (which is built into the drive).
Fuse Type Matters
AB's recommendations likely assume you are using specific types of fuses designed for motor circuits, such as:
Class CC
Compact, current-limiting fuses, often used for motor branch circuits.
Class J
Fast-acting, current-limiting fuses.
Class RK5
Time-delay fuses, designed to handle motor starting currents.
Class RK1
High performance time-delay fuses.
Semiconductor fuses: These fuses are specially designed to protect semiconductors and are often required for variable frequency drives (VFDs). They provide very fast overcurrent protection. Application Specifics
The 25-40A range suggests AB acknowledges different application needs (e.g., frequent starts/stops, heavy load profiles). A higher fuse within that range allows for those demanding applications.
Safety Factor
Manufacturers often include a safety factor in their recommendations to account for variations in installation practices and operating conditions.2.
NEC 430 Considerations (and Why the Straight Calculation Might Be Misleading)
430.52(C)(1) is a Maximum
Remember, 430.52(C)(1) gives you the maximum allowable short-circuit and ground-fault protective device (fuse or circuit breaker) for a motor branch circuit. It's NOT a requirement to use that maximum. You can use a smaller fuse, as long as it can handle the motor's starting current and prevent nuisance tripping.
Motor FLA vs. Drive Input Current
You're correctly using the motor's FLA (Full Load Amps) of 14A for your 430.52(C)(1) calculation. However, the drive's input current (18.4A in your example, per AB's documentation) is a crucial factor, especially when applying exceptions.
430.52(C)(1) Exception No. 1
This is where it gets interesting. It states that if the calculated fuse size (using the percentages in 430.52(C)(1)) does not correspond to a standard fuse size listed in 240.6, the next higher standard size shall be permitted.
430.52(C)(1) Exception No. 5 Where the motor starting current is conditional on the variable frequency drive (VFD) and the motor and drive are selected as a coordinated assembly, the overcurrent protection shall be permitted to be selected per the manufacturer’s instructions.
This is likely the path forward with your issue as many VFDs are used today, and the NEC realizes that drive manufacturers are much more specific to the requirements of the VFD. Always refer to the drive manual for specific requirements! NEC 430.130(A)(1) and the Drive
This section essentially extends the motor branch-circuit short-circuit and ground-fault protection requirements to the input side of the drive. It means you still need to consider 430.52(C)(1), but also the drive manufacturer's recommendations.
NEC 110.3(B) - Installation and Use
This is a CRITICAL section. It states that listed or labeled equipment (like your drive) must be installed and used in accordance with any instructions included in the listing or labeling. This means you MUST follow AB's instructions unless there's a clear and demonstrable code violation.
Here's how to reconcile and find the correct solution
Read the Drive Manual VERY Carefully
Pay close attention to the sections on: Input fuse requirements (type and ampacity). Short-circuit current rating (SCCR) of the drive. This is critical for selecting fuses that will protect the drive. Coordination tables (if provided). These tables will often specify the correct fuse for different motor sizes and supply voltages.2.
Identify the Fuse Type AB Recommends
The fuse type is just as important as the amperage. If the manual specifies a Class CC, J, RK5, RK1 or a Semiconductor fuse, it's designed to handle the inrush current of the drive and motor startup.3.
Consider the Drive's Input Current (Iin)
Your example has an Iin of 18.4A.
4.
Verify Fuse Ampacity with the Manual
If AB specifically states a 40A fuse of a certain class is required
This is likely because it has been specifically engineered as a coordinated system of components. 430.52(C)(1) exception No. 5 would allow you to use the manufacturers recommendation.
If AB provides a range (25-40A)
Start with the lower end (25A) and check if it causes nuisance tripping under normal starting and operating conditions. If so, incrementally increase the fuse size (within the recommended range) until you eliminate the nuisance tripping.5.
Document Your Reasoning
Keep a record of the following: Drive model number. Motor HP and FLA. Supply voltage. Selected fuse type and ampacity. Relevant sections of the NEC and the drive manual that support your selection.
Example Scenario
Let's say AB recommends a Class RK5 30-40A fuse for your application. Your calculations, based on the motor FLA alone, suggest a smaller fuse.
Start with the manufacturer's instructions
This is the most important step.*
Refer to NEC 430.52(C)(1) Exception No. 5
As mentioned previously this allows you to use the fuse as specified by the manufacturer.
In summary, while your calculations using the motor FLA are a good starting point, the drive manufacturer's instructions and the NEC exceptions specifically related to drives (especially 430.52(C)(1) Exception No. 5) are key to selecting the correct fuse. Always prioritize the manufacturer's recommendations (as required by NEC 110.3(B)) and carefully document your reasoning. Flag for review