Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 4 wire dryer Recept.

User: Raccoon 3, Location: Henrico County, VA

Asked on: Friday, April 17, 2009 at 5:49 pm EDT
Answered on: Sunday, May 12, 2024 at 4:59 pm EDT

Question: Where in code book does it state the requirement for 4 wire cord and Recept use for dryers and Ranges in single family dwellings.

2020 NECArticle 422.15 Appliance Receptacle Outlets(A) Cord-and-Plug Connected Appliances> 1. General. All cord-and-plug connected appliances shall be provided with a receptacle outlet having the following characteristics:> a) Voltage. The voltage of the receptacle outlet shall correspond to the voltage of the appliance to be connected.> b) Current. The rating of the receptacle outlet shall be not less than the maximum ampacity required by the appliance.> c) Receptacle Type. Receptacle outlets provided for the following appliances shall be identified for the specific appliance connection as follows:> i) Clothes Dryers—NEMA 10-30R> ii) Cooking Appliances—NEMA 14-30R, NEMA 14-50R, or NEMA 14-60RArticle 440.11 Receptacle Outlets(B) Counter Tops> 1. Circuits Required. At least two receptacle outlets shall be provided on the countertop surface one within 24 inches (610 mm) of each sink basin or countertop cooking appliance. Flag for review

Previous Question Next Question