User: Mike01, Location: MidWest
Asked on: Wednesday, June 1, 2011 at 6:31 pm EDT
Answered on: Tuesday, May 14, 2024 at 6:06 am EDT
Question: I have an application where the client wants power to test equipment in a specific room to be de-energized when the door to the space is opened, there are four disconnects that are located just outside the room I thought of either placing a contactor just ahead of the disconnect with door contacts on the door to open the contactors when the door is opened, another thought was to replace the disconnect with a molded case switch with shunt trip coil, the concern is the noise the contactors make everytime they cycle, I have never heard a contactor open and close just curious if they are ?noisy???
Noise Considerations
Yes, contactors can make noise when they operate. The noise level depends on the contactor's size, construction, and operating frequency.
Closing noise
When a contactor closes, it creates an arc that can generate a loud "pop" or "snap" sound.
Opening noise
When a contactor opens, the arc is extinguished, which can also produce a snapping sound.
Contact bounce
After opening or closing, the contactor's contacts may bounce several times before settling into their final position. This can create a rapid clicking or chattering noise.
Specific to Your Application
Using contactors
Placing contactors ahead of the disconnects and using door contacts to open them when the door is opened would create a noticeable noise each time the door is opened and closed.
Using molded case switches with shunt trip coils
Replacing the disconnects with molded case switches with shunt trip coils would eliminate the contactor noise.
Recommendation
Given the noise concerns, it would be best to use
molded case switches with shunt trip coils. This solution would provide a reliable and safe method of de-energizing the power when the door is opened without creating excessive noise.
Additional Considerations: Ensure that the molded case switches have the appropriate amperage and voltage ratings for your application. Use high-quality switches from a reputable manufacturer to minimize noise and ensure long-term reliability. Consider installing sound-dampening materials around the switches if necessary to reduce noise further. Flag for review