Topic: plug-in busway working space

User: alehman, Location: Lockport, IL

Asked on: Friday, June 3, 2011 at 10:15 am EDT
Answered on: Tuesday, May 14, 2024 at 6:09 am EDT

Question: We are contemplating installing plug-in busway for overhead distribution to server cabinets in a data center. Is working space per 110.26 required for:1. Busway feeder terminal boxes?2. Circuit breaker plug-in units?Thanks,Alan

  1. No2. Yes