Topic: Lug size

User: ptonsparky, Location: NE (9.06 miles @5.9 Degrees from Winged Horses)

Asked on: Monday, May 12, 2025 at 1:03 pm EDT
Answered on: Tuesday, May 13, 2025 at 8:24 pm EDT

Question: Any one know offhand what the max wire for the lugs on. CH BR2125 breaker? I have spare 3/0 AL............and a few more .

According to Eaton's BR series breaker specifications, the BR2125 (25 amp) breaker lug is rated for #14 - #4 AWG copper or aluminum wire.Therefore, 3/0 AL is too large for that breaker. You cannot safely and code-compliantly connect 3/0 aluminum wire to a CH BR2125 breaker. Flag for review