Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Emergency Lighting

User: Cleanis, Location: VA

Asked on: Tuesday, May 13, 2025 at 9:10 am EDT
Answered on: Tuesday, May 13, 2025 at 8:29 pm EDT

Question: Hello. I have a small restaurant/c-store. On the building plans we show 7 emergency exit lights with batteries. When power lost they all come on. The inspector wants emergency lights ahead of switch. So if the a room loses light the emergency lights will light. I'm dealing with four area that if something knocks out that room the emergency lights kick on.Thanks for your insight

Okay, I understand. The inspector wants to ensure that if the general lighting in a specific area fails (due to a switch being turned off, a breaker tripping, or some other issue impacting the regular lighting circuits), the emergency lights in that area immediately activate, regardless of whether the main power to the building is lost. This is a common and important safety requirement.Here's a breakdown of the problem and how to address it

Understanding the Inspector's Concern

The inspector is looking for localized emergency lighting functionality, not just building-wide power outage response. Think of it like this: Scenario 1: Building Power Outage

Your current system works. Main power goes out, all emergency lights come on. Great.


Scenario 2: Kitchen Circuit Breaker Trips

The lights in the kitchen suddenly go out, but the rest of the building has power. The inspector wants the emergency lights in the kitchen to come on IMMEDIATELY, even though the building's main power is fine. This is where your current setup is failing.

Why is this important?
Safety

People need to be able to see to safely exit, especially in areas like the kitchen with potential hazards (hot surfaces, equipment).


Code Compliance

Building codes (often based on the National Electrical Code - NEC) often require emergency lighting to be independent of the regular lighting circuits to address localized failures.

How to Achieve Localized Emergency Lighting Activation


Here are the common methods to achieve the desired functionality, along with considerations:1. Dual-Circuiting (Preferred)



Explanation

This is generally the "cleanest" and most reliable solution. It involves wiring the emergency lights to a separate circuit that is
not controlled by any local switches that control the regular lighting.

How it Works

Each emergency light has its own battery backup and is normally powered from a dedicated, unswitched circuit breaker panel. When the normal power on this circuit is present, the emergency light charges its battery and acts as a normal light. If that dedicated circuit fails (e.g., a breaker trips dedicated to emergency lights), the battery backup kicks in immediately.

Pros

Most reliable. Least likely to be accidentally disabled. Code compliant (when installed correctly).

Cons

Requires more wiring changes. May require adding a dedicated circuit to the breaker panel for emergency lights.2.

Using "Normal Power Sensing" Emergency Lights



Explanation

Some emergency light fixtures have a "normal power sensing" feature. They constantly monitor the voltage on the circuit they are connected to.


How it Works

The emergency light is wired to the same circuit as the normal lights in the area. If the voltage on that circuit drops below a certain threshold (e.g., the switch is turned off, a breaker trips), the emergency light automatically switches to battery power.

Pros

Simpler wiring compared to dual-circuiting.

Cons

The sensing circuitry must be reliable (ensure the lights are UL-listed and appropriate for commercial use). More susceptible to false triggers (e.g., voltage fluctuations). Could potentially be defeated (e.g., by intentionally tampering with the circuit). Requires emergency lights specifically designed for this feature.3.

Transfer Switch (Less Common, More Complex)



Explanation

A transfer switch monitors the voltage on the regular lighting circuit.

How it Works

If the voltage drops, the transfer switch disconnects the emergency lights from the regular circuit and connects them to a separate power source (typically the battery backup within the emergency light fixture).

Pros

Can be used with standard emergency light fixtures.

Cons

More complex installation. More components to fail. Generally not necessary for a small restaurant/c-store; overkill.

Steps to Take to Address the Inspector's Concerns


Talk to the Inspector

The best first step is to discuss the specific situation with the inspector. Ask for clarification on which areas they are concerned about and exactly what type of failure they are trying to protect against. Understanding their requirements is crucial.2.

Consult with a Licensed Electrician

You

must
use a qualified, licensed electrician. Emergency lighting is a critical life-safety system, and improper installation can have serious consequences. The electrician can assess your current wiring, determine the best solution (dual-circuiting or normal power sensing), and ensure the installation meets all applicable codes. Get several bids!3. Provide Electrical Plans and Specifications

Provide the electrician with a copy of your building plans, the electrical plans, and the emergency light specifications.4.

Get the Work Inspected

After the electrician completes the work, schedule another inspection to verify that the emergency lighting system meets all code requirements.5.

Testing and Documentation

Regularly test the emergency lighting system (monthly and annually). Keep a record of the tests. This is required by most codes.

Important Considerations



Code Compliance

Make sure the installation complies with all applicable building codes, fire codes, and electrical codes (typically based on the NEC). Your electrician is responsible for this.


UL Listing

All emergency lighting fixtures and components should be UL-listed (or equivalent) for the intended application.

Placement

Ensure that the emergency lights are strategically placed to provide adequate illumination along the egress path (the path people will take to exit the building). Typically this means along hallways, near exits, and in open areas.


Maintenance

Regularly inspect and test the emergency lights. Replace batteries as needed.

Example Scenario (Using Dual-Circuiting)

Let's say you have a kitchen with 3 emergency lights. Here's how dual-circuiting would work:1.

Current Situation

All the kitchen lights (including the emergency lights) are wired to the same circuit, controlled by a wall switch.2.

Dual-Circuiting Solution

The electrician runs a new, dedicated circuit from the breaker panel directly to the emergency lights. This circuit is not connected to any switches. The electrician disconnects the emergency lights from the original lighting circuit.* Now, the emergency lights are powered by the dedicated, unswitched circuit. They will automatically switch to battery power if that dedicated circuit fails.

In summary, to meet the inspector's requirements, you will most likely need to modify your wiring to ensure that the emergency lights come on immediately when the regular lights in a given area fail, regardless of the building's overall power status. Consulting with a licensed electrician is essential for a safe and code-compliant installation.
Flag for review

Previous Question View on the official Mike Holt Forum Next Question