Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Class II Div 2

User: gadfly56, Location: New Jersey

Asked on: Friday, June 6, 2025 at 4:26 pm EDT
Answered on: Friday, June 6, 2025 at 4:27 pm EDT

Question: Are there any practical differences between the wiring methods used for Class I Div 2 and Class II Div 2? What about receptacles and equipment? I have a nutraceutical operation trying to close out a fire alarm permit (not ours) and it looks like the room is, per the drawings, Class II Div 2. The fire alarm equipment is definitely not rated. I can put in some dual listed equipment, but was hoping to get guidance on some path closer to Class II.

Okay, let's break down the wiring methods and equipment requirements for Class I Division 2 and Class II Division 2 locations, and then discuss your situation with the fire alarm permit.

Understanding the Key Differences and Similarities

The fundamental difference is the type of hazard: Class I: Flammable Gases or Vapors

The risk is from the presence of flammable gases or vapors in the air.


Class II: Combustible Dusts

The risk is from the presence of combustible dust in the air.While both Division 2 locations have a reduced risk compared to Division 1 (where the hazard is normally present), the ignition mechanisms are different. Gases are ignited by flames, sparks, or hot surfaces. Dusts can be ignited by flames, sparks, hot surfaces and by high surface temperatures due to layer formation.

Wiring Methods: Significant Differences
Class I, Division 2



General

Wiring methods must prevent the ignition of flammable vapors.

Acceptable Methods

Rigid Metal Conduit (RMC) Intermediate Metal Conduit (IMC) Type MC cable with listed fittings. (Can be used if cable is approved for the location) Type TC-ER cable with listed fittings. Cable Seal requirements may apply at the boundary of the classified area to prevent the propagation of flammable vapors. Check section 501.15 in the NEC.

Important Note

Explosionproof enclosures are generally NOT required for Class I, Division 2. The goal is to prevent ignition sources.


Class II, Division 2



General

Wiring methods must prevent the ignition of combustible dust. Dust-tight construction is key.


Acceptable Methods

Rigid Metal Conduit (RMC) with threaded dust-tight fittings. Intermediate Metal Conduit (IMC) with threaded dust-tight fittings. Type MC cable with listed dust-tight fittings. (Check cable markings to make sure it's suitable) Type TC-ER cable with listed dust-tight fittings.

Dust-Tight Seal Fittings

May be needed, especially at the entry to enclosures, to prevent dust from entering the raceway system and potentially creating a hazard elsewhere.


Important Note

The focus in Class II, Division 2 is on preventing dust from accumulating within the wiring system and preventing hot surfaces.

Receptacles and Equipment: Critical Differences
Class I, Division 2



Requirements

Equipment must be designed to prevent ignition of flammable vapors.

Acceptable Types

Equipment listed for Class I, Division 2. Enclosed and gasketed equipment that prevents the escape of sparks or hot metal. Non-incendive equipment Purged and Pressurized Equipment

Receptacles

Receptacles must be designed to prevent the release of sparks. Use listed Class I, Division 2 receptacles with suitable plugs.

Class II, Division 2



Requirements

Equipment must be designed to prevent ignition of combustible dust. Surface temperature is a major factor.

Acceptable Types

Equipment listed for Class II, Division 2. Equipment that is dust-ignitionproof. This means the enclosure is designed to prevent dust from entering and to withstand an internal dust explosion. The surface temperature of the equipment must be below the ignition temperature of the specific dust that is present. This is critical. The equipment listing will specify the maximum surface temperature. Purged and Pressurized Equipment

Receptacles

Use listed Class II, Division 2 receptacles with suitable plugs. They must be dust-tight and designed to prevent sparking.

Why This Matters to Your Fire Alarm Permit


The fire alarm equipment must be listed and approved for Class II, Division 2 locations. Here's why a simple "dual listing" for Class I Div 2 won't cut it:1. Dust-Tightness

Class II, Div 2 equipment must be dust-tight to prevent dust ingress. Class I, Div 2 equipment might not be. Dust accumulation inside can lead to overheating and ignition.2.

Surface Temperature

Class II, Div 2 equipment has stringent surface temperature limits to prevent dust ignition. Class I, Div 2 equipment may not have the same temperature limits.3.

Explosion Containment (Dust-Ignitionproof)

Class II Div 2 equipment is usually constructed with a "dust ignition proof" enclosure.

Your Options and a Path Closer to Class II Compliance
1. Confirm the Classification

Absolutely confirm the Class II, Division 2 designation. This requires a qualified person (often a professional engineer) to assess the area and determine the appropriate classification. Review the basis of design to fully understand the area classification. Dust explosion hazard is commonly overestimated or applied incorrectly. Is there actually a likelihood of enough dust to cause an explosion?2.

Search for Class II, Division 2 Fire Alarm Equipment

This is the most straightforward (but possibly most expensive) approach. Contact fire alarm system manufacturers and specifically ask for equipment listed for Class II, Division 2.3.

Purging and Pressurization

If suitable Class II, Div 2 fire alarm equipment is unavailable, you could consider purging and pressurization. This involves enclosing the fire alarm equipment in a suitable enclosure and maintaining positive pressure with clean air or inert gas. This is complex and requires ongoing maintenance. This might be considered if you have a central fire alarm panel located inside the area, but could be cumbersome.4.

Relocation

Can the fire alarm control panel be moved outside the Class II, Division 2 area? If so, only the initiating devices (smoke detectors, heat detectors, pull stations) need to be rated. However, initiating devices still need to be suitable for the location.5.

Appeal to the Authority Having Jurisdiction (AHJ)

This is a last resort, but if you can demonstrate that the actual dust hazard is minimal (e.g., through improved dust control measures, regular cleaning, or limited material), you might be able to persuade the AHJ (local inspector) to accept alternative protection methods. This will require careful documentation and a strong justification, and is unlikely to be successful.

Steps to Take Immediately


STOP WORK

Do not proceed with installing non-rated equipment.2.

Review Drawings

Thoroughly review the drawings. Look for the area classification and any notes about hazardous locations.3.

Engage a Qualified Professional

Hire a qualified electrical engineer or hazardous location expert. They can: Verify the area classification. Advise on suitable equipment and wiring methods. Help you develop a compliance strategy. Interface with the AHJ.4.

Contact Fire Alarm System Manufacturers

Inquire about Class II, Division 2 equipment.5.

Document Everything

Keep detailed records of your assessments, communications, and decisions.

Important Considerations



Dust Characteristics

The type of dust (e.g., sugar, flour, metal) matters. Different dusts have different ignition temperatures and explosion characteristics. You need to know
exactly what dust is present in the nutraceutical operation.

Dust Control

What dust control measures are in place (e.g., ventilation, dust collection systems)? Are they effective? Proper dust control can sometimes reduce the classification level of an area (but don't rely on this without expert consultation).*

Cleaning

How frequently is the area cleaned to remove accumulated dust? Regular cleaning is crucial in Class II locations.

In summary,
using equipment only rated for Class I Div 2 in a Class II Div 2 location is not a viable or safe option. You must address the specific hazards associated with combustible dust. Engage a qualified professional to guide you through the compliance process. Flag for review

Previous Question View on the official Mike Holt Forum Next Question