User: MFS-PDX-313, Location: Tualatin, Oregon, USA
Asked on: Friday, June 27, 2025 at 12:06 pm EDT
Answered on: Friday, June 27, 2025 at 12:06 pm EDT
Question: Years back, the company I work for had a third-party inspection for a number of standards on a piece of industrial equipment. One of them was NFPA79.One of the findings was that we had a problem with one of the compartments of the equipment. In this compartment was an electrical panel with I/O (specifically, it was Omron brand I/O cards with an Ethernet coupler for communicating back to the PLC), various piping for compressed air and nitrogen (along with solenoid valves), and a couple of 2kW 208VAC pump controllers.The inspector stated that due to NFPA79 11.2.2.2 "Pipelines, tubing, or devices (e.g., solenoid valves) for handling air, gases, or liquids shall not be located in enclosures or compartments containing electrical control equipment." we had to remove the pump controllers.We were still able to keep the I/O in that compartment.Now unfortunately, the engineer who handled that safety audit is no longer with us and didn't document the audit very well. Or if he did, his laptop was scrubbed and we don't have the documents. All I have is an old email stating the above.Can someone explain why we were able to keep the I/O in that compartment? It seems as though the above mentioned part of NFPA79 would restrict us from having anything electrical in that compartment. Is it because all the I/O is 24VDC?Also, if this question is better suited in a different forum, let me know, and I can move it.
You're right to question this, as the interpretation seems inconsistent. Here's a breakdown of NFPA 79 11.2.
2.2 and why your I/O may have been allowed to stay
Understanding NFPA 79 11.2.
2.2
The core of this section is about segregation of fluids and electrical components. The goal is to prevent flammable, corrosive, or conductive fluids from damaging or interfering with electrical components, potentially causing: Electrical shock hazards
Fluids can conduct electricity, creating shock risks.
Fire hazards
Flammable fluids near electrical arcs or heat sources are dangerous.
Corrosion and damage
Fluids can corrode or damage electrical components, leading to failures.
Reduced reliability
Fluid contamination can cause malfunctions.
Why the Pump Controllers Had to Go
Based on the information you've provided, the 2kW 208VAC pump controllers almost certainly had to be moved for these reasons: Voltage Level
They operate at 208VAC, a significant voltage that poses a greater shock and fire hazard if exposed to fluids.
Power Level
2kW is a substantial power level, meaning a fault could result in a significant electrical arc and a higher risk of ignition if flammable fluids are present.
Possible Explanations for Keeping the I/O
Here are the most likely reasons why the I/O was allowed to stay, despite the general prohibition in NFPA 79 11.2.
2.2:1. Low Voltage and Limited Energy
The most probable explanation is the low voltage (24VDC) and limited energy of the I/O cards. A 24VDC circuit, especially one with limited current, poses a much lower shock and fire hazard compared to a 208VAC, 2kW pump controller. NFPA 79 aims to mitigate significant electrical hazards related to fluid exposure. Small control signals at low voltage are generally considered less risky.2.
Enclosure Rating and Fluid Containment
The inspector may have considered the
enclosure rating and the likelihood of fluid leaks. If the enclosure was rated to protect against fluid ingress (e.g., NEMA 4/IP66), and the piping and valves were installed with a very low risk of leaks (e.g., using robust fittings and materials compatible with the fluids), the risk might have been deemed acceptable for the low-voltage I/O.3. Risk Assessment and Mitigation
The inspector might have performed a risk assessment that considered the specific installation, the types of fluids, the likelihood of leaks, and the potential consequences. If the risk was deemed low, even with the I/O present, it could have been acceptable. However, this would typically require documentation of the risk assessment.4.
Alternative Interpretation (Less Likely)
It's possible (but less likely) that the inspector interpreted the rule very strictly to only exclude devices handling the fluids themselves. The I/O, while being electrical, isn't directly involved in the handling of air, gases, or liquids. This is a weaker argument, but depending on the inspector's approach, it could have been a factor.
Important Considerations Authority Having Jurisdiction (AHJ)
The ultimate interpretation of NFPA 79 lies with the AHJ (the inspection authority). It's possible the inspector had a specific reason or local interpretation that influenced the decision.
Documentation
The lack of documentation is a significant problem. You need a clear record of the safety audit findings and rationale.
Current NFPA 79 Edition
Ensure you're working with the latest edition of NFPA 79. Standards are updated regularly, and requirements may have changed.
Machine-Specific Risk Assessment
Even if the I/O was deemed acceptable in the past, a new risk assessment is advisable, especially if the machine has been modified or if you have any doubts about the safety of the current configuration.
Local Codes and Regulations
Be aware of any local electrical codes or regulations that might supplement or supersede NFPA 79.
Recommendations1. Consult a Qualified Electrical Safety Professional
The best course of action is to consult a qualified electrical safety professional with expertise in NFPA 79 and industrial machinery. They can perform a new risk assessment and provide guidance on compliance.2.
Review the Installation
Carefully examine the installation of the I/O, piping, and valves. Look for any signs of potential leaks or damage.3.
Document Everything
Meticulously document all safety-related decisions, risk assessments, and justifications.4.
Consider Separation Even for Low Voltage: Even if the I/O is technically compliant, consider whether you can reasonably relocate it to a separate compartment to improve safety and reduce the risk of fluid contamination.In summary, while NFPA 79 generally prohibits mixing fluids and electrical equipment, the low voltage and limited energy of the I/O likely played a significant role in the inspector's decision to allow it to remain in the compartment. However, without proper documentation, it's impossible to know the exact rationale. Consulting a qualified safety professional is strongly recommended to ensure compliance and safety. Flag for review