Question: Do any motors under 1hp require overload protection or could I just put it on a hp rated switch fed by a breaker and be ok? Next question I see many exhaust fans in Industrial plants that are normally fed by a breaker and then a snap switch at the fan itself do the snap switches have to have integral overloads for that to be ok?

Let's break down motor overload protection, horsepower ratings, and the specific case of exhaust fans.

Motor Overload Protection Under 1 HP

Yes, motors under 1 HP absolutely require overload protection. This is a critical safety measure to prevent motor burnout and potential fire hazards.Here's why: NEC Mandate

The National Electrical Code (NEC) provides specific requirements for motor overload protection, regardless of the motor's horsepower rating. While the rules may be slightly less stringent for small motors, protection is still mandatory.


Overload vs. Short Circuit

A circuit breaker provides short-circuit protection (rapidly interrupts a high-current fault). It does not provide adequate overload protection. An overload is a sustained current draw above the motor's rated current, but below the level that would trip a standard breaker immediately. Overloads cause motors to overheat and fail prematurely.

Why Overload Protection Matters

Motors are designed to operate at their rated current. Conditions that can cause an overload include:
Mechanical binding or excessive load. Low voltage. Improper ventilation. Failure of internal motor components.

Methods for Overload Protection (Under 1 HP)


Integral Thermal Protection

Many small motors (especially those in appliances or tools) have built-in thermal protectors. These devices sense the motor's internal temperature and automatically shut off the motor if it overheats. They reset automatically (after the motor cools down) or require manual reset. Motors with integral protection are often marked as such.2.

Separate Overload Relay

For motors
without integral protection, you must provide an external overload relay. This device is designed to trip at a current slightly above the motor's full-load amperage (FLA) and will de-energize the motor circuit. These relays are often adjustable to match the motor's FLA.

Important Considerations When Selecting Overload Protection



Motor FLA

The motor's full-load amperage (FLA) is the most important factor in selecting the correct overload protection. The overload device must be sized to trip within a reasonable time at a current slightly above the FLA.

Service Factor

If the motor has a service factor greater than 1.0, you might be able to adjust the overload protection slightly higher, but always consult the NEC and manufacturer's recommendations.

Horsepower-Rated Switch and Breaker

Simply putting a motor on a horsepower-rated switch and feeding it with a breaker is
not sufficient overload protection. The breaker primarily protects against short circuits. The horsepower-rated switch is sized to handle the inrush current when the motor starts, but it doesn't actively protect against overloads.

Exhaust Fans in Industrial Plants: Snap Switches


The situation with exhaust fans and snap switches is common, but requires careful consideration.
Snap Switches and Overload Protection

Standard snap switches (the common light switch type) generally do not have built-in overload protection. Therefore, if the fan motor doesn't have integral overload protection, and the snap switch is the only switching device after the breaker, this configuration violates NEC requirements.

Acceptable Scenarios (with Snap Switches)


Motor with Integral Overload Protection

If the fan motor has built-in thermal protection (as described above), the snap switch is acceptable. The motor will shut itself off if it overheats. This
must be verified; look for markings on the motor.2.

Separate Overload Relay

A properly sized overload relay is installed
before the snap switch. The overload relay will trip and de-energize the motor circuit if an overload occurs.

Alternatives to Snap Switches



Motor Starter with Overload Protection

A motor starter combines the switching function with overload protection. This is a very common and reliable solution.


Combination Motor Starter

Includes a disconnect switch or breaker and overload protection in a single enclosure.

In summary

Motors always need overload protection, regardless of horsepower. A breaker alone does not provide overload protection. Snap switches in exhaust fan circuits are only acceptable if the motor has integral overload protection or a separate overload relay is installed. Consult the NEC and the motor manufacturer's specifications for specific requirements. When in doubt, err on the side of caution and install proper overload protection. It's a small price to pay for safety and extending the life of your motor.