User: Strombea, Location: Prescott, Arizona, USA
Asked on: Monday, August 11, 2025 at 11:58 am EDT
Answered on: Monday, August 11, 2025 at 11:59 am EDT
Question: So I know that a standard breaker is rated for 80% of its rating and 100% rated breakers are rated with an approved assembly for 100% continuous load.But my question is with Non Continuous loads on a standard breaker. Is it still only 80%? And if so does that mean that there are 2 different deratings for the same load?20 amp breaker can be loaded to 16 amps ...But continuous loads need to be calculated first.So a 14 amp wall heater @ 125% = 17.5 amps (more than 16) Can NOT be on a 20 amp breaker even though the 125% has already been accounted for. (its only pulling 14 amps)I think the answer to my question is that there are 2 different rules happening here and they both have to be done to comply.And with a 100% rated breaker... do you still need to add the 125% to a continuous load first as it is a different rule than the breaker rule? (the heater is still seen as 17.5 amps... NOT 14 amps)Side question: Is a 100% rated breaker the same thing as a fully rated breaker in a series/fully rated system, or are these different products, Meaning if you wanted to not series rate and it was a continous load, do they make that combination in a breaker?
You're asking about a critical, and often misunderstood, aspect of electrical circuit design. Let's break down the concepts
Understanding the 80% Rule and Continuous Loads
80% Rule (Standard Breakers)
Standard circuit breakers are designed to not be loaded to their full capacity for extended periods. The 80% rule, stipulated by the NEC (National Electrical Code), dictates that you should not load a standard breaker to more than 80% of its rating for a
continuous load. This is because the breaker and associated wiring heat up over time. The 80% rule acts as a safety margin to prevent nuisance tripping and potential hazards. This is found in NEC 210.19(A)(1) and 210.20(A). Continuous Load
A continuous load is defined as a load where the maximum current is expected to continue for 3 hours or more. Common examples include lighting, heating, and motors that run for extended periods. NEC 210.20(C) is where this definition resides.
Non-Continuous Loads
These are loads that operate for less than 3 hours. Examples include appliances used intermittently, power tools, or lighting in rooms where lights are not constantly on.
Answering Your Core Questions
Non-Continuous Loads and the 80% Rule
No, the 80% rule does not apply to non-continuous loads by definition. You can load a standard breaker up to its full rated amperage (100%) with only non-continuous loads. However, remember the breaker and wire sizes must still be sized appropriately for those loads.2.
Two Different Deratings? Yes, you are correct that there are two separate considerations: Continuous Load Calculation (125%)
NEC 210.19(A)(1) and 210.20(A) require that for continuous loads, the overcurrent protection (breaker or fuse) and conductors be rated for at least 125% of the continuous load. You're essentially "sizing up" the components. You apply the 125% before you consider the 80% rule, as it is a separate calculation.
80% Rule (Standard Breakers)
This rule dictates that the actual load on the breaker cannot exceed 80% of its rating if there is a continuous load.3.
Your Heater Example (14 Amp, Continuous)
Your analysis is correct. Let's reiterate why: The heater is considered a continuous load. 14 amps 1.25 = 17.5 amps (this is the minimum breaker and wire ampacity required) A 20-amp standard breaker can only handle 16 amps continuously (20 amps 0.8 = 16 amps). Therefore, a 20-amp standard breaker is not suitable for this continuous 14-amp load. You would need a higher amperage breaker and appropriately sized wiring (likely a 25 amp breaker with 10 AWG wire).4.
100% Rated Breakers and the 125% Rule
Yes, you still need to apply the 125% rule for continuous loads, even with a 100% rated breaker. The 125% factor addresses the conductor's ability to handle the continuous current without overheating. The 100% rated breaker simply means it can be loaded to its full nameplate rating after the 125% rule has been applied and that is also approved to do so via its listing. The heater (14 amps) is still considered a 17.5 amp load for wire sizing. The 100% rated breaker allows you to use a breaker closer to the calculated load, but only when part of a fully tested and approved assembly.
Side Question: 100% Rated Breakers vs. Fully Rated Systems 100% Rated Breakers
As discussed above, these breakers, when part of a tested and approved assembly, can be loaded to their full nameplate rating, after the 125% factor for continuous loads has been considered. They are designed to dissipate heat more efficiently.
Fully Rated Systems (Series Rated Systems)
This is a different concept. It refers to the interrupting rating of circuit breakers in a system. In a fully rated system, each breaker has an interrupting rating sufficient to handle the maximum available fault current at its location in the system, without relying on another breaker upstream to help interrupt the fault. A fully rated system does not require all breakers to be 100% rated, nor are they always associated with continuous loads.
Series Rated Systems
To simplify, series rating allows a downstream breaker with a lower interrupting rating to be used, relying on an upstream breaker with a higher interrupting rating to assist in clearing a fault. This is generally less expensive but requires careful coordination studies to ensure proper operation.
Combining 100% Rated Breakers and Fully Rated Systems
Yes, you can have a fully rated system that also utilizes 100% rated breakers for continuous loads. They are independent concepts. You would choose 100% rated breakers to better handle continuous loads (and save on breaker size and panel space) and design a fully rated system to ensure sufficient interrupting capacity throughout your electrical distribution system.
In Summary Think of the 125% rule for continuous loads as a sizing requirement for the conductors and overcurrent protection. The 80% rule for standard breakers is a loading restriction. 100% rated breakers allow you to load the breaker closer to its nameplate rating, but you still need to apply the 125% rule to determine the minimum conductor size and breaker rating.* Fully rated (and series rated) systems relate to interrupting ratings, not continuous load handling.Consult a qualified electrical engineer or electrician for your specific application to ensure compliance with the NEC and all applicable codes and standards. The information above is for educational purposes and should not be considered a substitute for professional advice. Flag for review